    Water condensation from Unico Jigh Velocity

    We have a Unico high velocity system installed four years ago and from the beginning we have had noise and condensation issues. The contractor came back to seal the outlets with silicone but this problem has not gone away. Now he contractor refuses to answer our calls. We are otherwise very happy with the unit for cooling and air crclaton as well as heating

    We called in a separate contractor and they have identified the problem to be the lack of length f attenuating tube. It seems that the original installer cut xcorners and tried to use less material and did not follow the installation instructions.

    The new contractor is having a really hard time finding a supplier of the Unico attenuating tube. We need approximately 100 feet. Would someone be able to help me out as to where I can purchase 100 feet of attenuating tube for this Unico system? Thank you

  2. #2
    Join Date
    Apr 2014
    Posts
    5
    Post Likes
    Hi Mike,

    I apologize for the issues you're experiencing.

    Please give us call at 800-527-0896 and ask for Brian.

    I can help you and your contractor locate the sound attenuator and also talk about the condensation problem.

    Thank you.

  3. #3
    Join Date
    Jul 2016
    Posts
    8
    Post Likes
    Thread Starter

    Smile Thank you

    Quote Originally Posted by Unico System View Post
    Hi Mike,

    I apologize for the issues you're experiencing.

    Please give us call at 800-527-0896 and ask for Brian.

    I can help you and your contractor locate the sound attenuator and also talk about the condensation problem.

    Thank you.
    Thank you Bryan for speaking with a local contractor and give connecting him with one of the distributors of the product we need. Also thank you for your input on how to apply the fix. I will keep you up to date on how it goes.

    Thank again

  4. #4
    Join Date
    Jul 2016
    Posts
    8
    Post Likes
    Thread Starter
    A big thank you to Unico for coordinating with a local contractor who installed additional attenuating tubes and our system is working fantastic...there seems to be no more condensation, although the spring will be a tell tale, and in addition, noise has been considerably reduced. Thank you Bryan once more!

  5. #5
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    3,631
    Post Likes
    Mike,there was/is a condensation problem this time of the year? Hats off to Unico for stepping up and getting involved.

  6. #6
    Join Date
    Jul 2016
    Posts
    8
    Post Likes
    Thread Starter
    We live in Canada and the condensation would happen in the spring for some reason. We were very pleased with Unico. In the end the problem was the actual installation where the installer took shortcuts and didn't install the recommended length of attenuating tube. We had a different heating and cooling company look at it and they identified the problem quickly and once we were able to procure the product they installed it according to the company's recommendations.

  7. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    3,631
    Post Likes
    I had no idea that the sound attenuating ducting had control over humidity. Now ,no insulation is a condensing matter.

  8. #8
    Join Date
    Jul 2016
    Posts
    8
    Post Likes
    Thread Starter
    I didn't either, and just to make sure we are also adding more insulation


    Sent from my iPhone using Tapatalk