  1. #27
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    He pumped it down to check the sight glass .... duh .... didnt you read his post ?



  2. #28
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    Tempco .... tell your Boss he's having a blonde moment and needs to listen to the internet , because the internet is always right !

    Told you no need to check screen ? really ?

    Boss go stand in the corner !!

  3. #29
    Join Date
    Dec 2011
    Location
    Western Kentucky
    Posts
    44
    Sorry snap I must have overlooked that part.

    Tempco.. After ur boss learns his lesson you can take him out of timeout. Jk!!

    I will assume you checked the sight glass b4 pumping system down and it was full, not bubbling which may indicate a low charge.

    If you are still having same issues and confident charge is ok, I would suggest pumping system down, checking screen or other possible restrictions. If you find no evidence of restriction then I would replace txv and lld. Leak test, vacuum and then see where you are.

    Someone more experienced please correct me if I gave bad advice as I am still very new in the saddle

    Good luck tempco

  4. #30
    Join Date
    Aug 2012
    Posts
    21
    yes cant tell sometimes if site is full or not...system has a pump down service switch...yes site full and not bubbling...as I mentioned this store is less than 5 years old with all new equipment...

  5. #31
    Join Date
    Feb 2013
    Location
    Australia, NSW
    Posts
    5
    have you done a stall test on the fan in the end that is freezing? ive had this before, where everytime ive opend the case the fan is spinning, but after a few checks over a week i found the fan could be stoped with my screwdriver, after watching it over an hour i found the fan would slow down and sometimes stop, then speed up again.

    replaced the fan havent been back for that case since.

  6. #32
    Join Date
    Dec 2008
    Location
    NW Iowa
    Posts
    125
    Quote Originally Posted by TempcoDog View Post
    Pumped down and checked sight. Checked SH as per manufacturer instructions. Everything bang on. My mistake on the defrost. it is 4 times a day for 40 minutes off time. Removed product, shelves and panel. Heavy build up of ice on back of coil almost all he way but mainly the first half as I mentioned. Cleaned all that up. Stat has been acting erratic for awhile so we decided to change it. Boss said no at this time to checking screen. My guts with you chappa on the screen. Guess we will see what happens
    Thats crazy, I would check the screen on txv.

  7. #33
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    Quote Originally Posted by Muz View Post
    have you done a stall test on the fan in the end that is freezing? i found the fan could be stopped with my screwdriver.
    Muz .... umm ... have you been taking too many them little blue pills again ?? Put the Screwdriver down buddy ...

  8. #34
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,621
    Quote Originally Posted by Snapperhead View Post
    Muz .... umm ... have you been taking too many them little blue pills again ?? Put the Screwdriver down buddy ...
    Yeah, God gave you perfectly good fingers to do a "stall" test If you see blood, motor is ok
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  9. #35
    Join Date
    Aug 2012
    Posts
    21
    If we suspect a restriction we are changing the TXV. It's sweat no flare

  10. #36
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,670
    Quote Originally Posted by TempcoDog View Post
    If we suspect a restriction we are changing the TXV. It's sweat no flare
    IMO, this is a big waste of time, effort and money.

    In refrigeration, the TEV is considered to be a serviceable part.

    Take it apart, clean it, service it (replace a power element if needed)

    Full on replacement is really only required if the body is leaking or there is damage to the internal components.

  11. #37
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    3 pages and hardly a mention of SH......wow.

  12. #38
    Join Date
    Aug 2012
    Posts
    21
    Yes I did in post #24. And JP if you remove the TXV and service it and even change power head why not just replace it? For the cost of time to sweat it out ( even better if they are flare), re- install, vacuum, etc and just a couple hundred more to replace. I've replace a few that had leaks in the body already in my short career.

  13. #39
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by TempcoDog View Post
    Yes I did in post #24.
    Which is why the word 'hardly' was chosen instead of 'not'. ;-)

Page 3 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event