Thread: open dairy half coil freezing
-
02-11-2013, 01:55 PM #40
depends .... if its a customer who always complains " dat bill too spensive " its getting cleaned.
If they pay their bills without question , give them a shiny new Txv if the supply house is near by
-
02-11-2013, 06:34 PM #41
Professional Member
- Join Date
- Jul 2011
- Location
- Lehigh Valley, PA
- Posts
- 226
Regarding the defrost, are there electric elements or is this air defrost? If electric, I'd be testing that circuit right after I thawed the ice. Hell with taking apart a TXV until I knew if the unit was defrosting correctly.
-
02-11-2013, 09:38 PM #42
-
02-11-2013, 09:40 PM #43
-
02-15-2013, 10:50 AM #44
Professional Member
- Join Date
- Dec 2009
- Posts
- 132
We recently had a problem at a grocery store where half of the coil would freeze up. We found that the filter for the ambient air curtain was plugged solid. The cold air would drop to the floor, freeze the water in the drain line and ice up half the coil. We cleaned the filters and have not had a problem since.
-
02-22-2013, 10:24 AM #45
If drain pan doesn't clear fast enough you will see ice on the cold side of the case. Open cases (headaches) are the garbage collectors where the grape seeds,gum,etc. wind up. The case drain flushed ok? A long time back when the same thing was happening to me on a new case I finally got mad enuf to empty the whole case and found an air drill under the fan shroud. The cold side of the case will ice up first even if all is clear on that side.
-
02-22-2013, 09:13 PM #46
Regular Guest
- Join Date
- Aug 2012
- Posts
- 21
That's interesting Neil. Yes lots of crap collects and the adjoining case had a plugged drain last week. But my case in question has been good. Once I took panels Nd shelves off I discovered a very large build up of ice on back side of coil. Spent some time defrosting it
-
02-25-2013, 09:28 AM #47
Pro-Rep Member
- Join Date
- Jul 2011
- Location
- St. Louis
- Posts
- 99
Shouldn't there be a divider (plastic wall) between the two cases to prevent what happens in one to affect the other?
In an infinite universe, not only are all things possible, all things are necessary
-
02-25-2013, 09:44 PM #48
-
02-25-2013, 11:37 PM #49
Abnormal moisture will always find a way to plug things up
-
02-26-2013, 08:55 AM #50
Pro-Rep Member
- Join Date
- Jul 2011
- Location
- St. Louis
- Posts
- 99
Of course you are right, cases in supermarkets with common suction groups would not be divided. Since these two cases are on separate condensing units, I wonder if the warmer air from one case in defrost (even just off cycle) could affect the thermostat of the other case and cause it to overcool.
Just a thought.In an infinite universe, not only are all things possible, all things are necessary
-
02-26-2013, 06:58 PM #51
-
02-26-2013, 08:03 PM #52
I'm going back a bit here, but about 30 years ago Hussmann (I believe) required dividers between gas & electric defrost cases on different circuits or systems and recommended them for all others.
I haven't found any current requirements...but that doesn't mean there aren't any.