That would have been the first thing i would of checked.
-
02-02-2013, 01:21 PM #16
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
How many defrosts? For how long?
-
02-02-2013, 03:52 PM #17
Regular Guest
- Join Date
- Aug 2012
- Posts
- 21
Thanks guys
It's a hill Phoenix 05DMH12
Off time defrost 6 times daily can't remember for how long. But it was fine for 3-4 years since installed new
What I read they want 6-8 SH at bulb. I will first check sight!
Yes low charge or tx problem now that I've read some info. And I now learned a tx was replaced in the case beside it last year. Coincidence?!
-
02-02-2013, 07:02 PM #18

Last thing I would admit ..... is I forgot to check sight glass
LIE if you have to ; )
First thing I do when walking up to a unit is check coil for cleanliness , then locate the SG
-
02-02-2013, 07:06 PM #19
http://www.hillphoenix.com/wp-conten...h.pdf?inline=1
That ought to link you to the manual
-
02-03-2013, 08:38 AM #20
Regular Guest
- Join Date
- Dec 2008
- Location
- NW Iowa
- Posts
- 39
-
02-03-2013, 04:20 PM #21
Regular Guest
- Join Date
- Aug 2012
- Posts
- 21
what can I say snapper I'm a terrible lier!...I do know both coils are clean...screens..I'm assuming in the TX?
-
02-04-2013, 05:49 PM #22
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
Yep pump it down and check the screen after you check the sight glass...
6 defrosts sounds like a lot for a hill Phoenix most of the newer ones I've installed are 4 defrosts for about 45 mins... But check your model with that link the JP put up.
-
02-04-2013, 05:53 PM #23
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
Never mind I see you posted your model, looks like 4 for 42 minutes.
-
02-04-2013, 08:50 PM #24
Regular Guest
- Join Date
- Aug 2012
- Posts
- 21
Pumped down and checked sight. Checked SH as per manufacturer instructions. Everything bang on. My mistake on the defrost. it is 4 times a day for 40 minutes off time. Removed product, shelves and panel. Heavy build up of ice on back of coil almost all he way but mainly the first half as I mentioned. Cleaned all that up. Stat has been acting erratic for awhile so we decided to change it. Boss said no at this time to checking screen. My guts with you chappa on the screen. Guess we will see what happens
-
02-04-2013, 09:20 PM #25
-
02-04-2013, 09:44 PM #26
Professional Member
- Join Date
- Dec 2011
- Location
- Western Kentucky
- Posts
- 38
I'm confused!!
What exactly was the purpose for pumping system down??