    customer has a 24 foot and 12 foot open coolers side by side. the 12 foot has been having issues for last couple months. one call it was to warm. then month later to cold. problem now is approx half the coil is iced up. its the left side where the TXV feed the coil and it's beside the 24 foot. the 24 and the other 6 feet of the 12 foot are running fine. good airflow and temp. The iced side is of course warm and bad airflow due to the ice up. all fans are running. checked TXV and it seems fine.. system has off time defrost which I confirmed is working
    this one seems wierd to me...if it was the TXV wouldn't the far end of the coil be warm cause it would be starving??
    I'm thinking its the thermostat... I turn dial up and down and I can hear it click and see TXV feed... thermostat sensing bulb is near middle..My thought is the bulb has failed.
    anyone else expience same or similar??
    Dec 2008
    New York, ny
    You made sure that the fan is definitely running??
    Maybe its turning only because the other fan is making it turn.
    Sent from my SGH-T999 using Tapatalk 2
    Jun 2006
    My first thought without knowing specifics, is you are low on charge. Verify proper charge.
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by frio View Post
    Without any other info this is what I'm thinking
    No the fan/ fans are definitely running. I checked motors etc. they are definately operational. less than 5 year old hill pheniox systems. Roof top air cooled condensers. This 12 foot is on its own as is the 24 foot. They are all open as if its a 36 foot unit.
    Low charge? Iced where it feeds but normal at the far end of the coil? Doesn't seem so to me as his system has been problematic for awhile
    Dec 2011
    Western Kentucky
    Does the 12 foot section have just one txv??
    Dec 2011
    Western Kentucky
    Is sight glass clear??
    Dec 2008
    New York, ny
    On the open case they some times have a motor on top t cause the curtain effect maybe that motor is no good?
    Quote Originally Posted by TempcoDog View Post
    >snip<
    This adds up to me.
    Here's what ya do.
    http://www.sporlanonline.com/90-30-1.htm
    read that document, then follow it as far as charging suggestions.
    A motor up top too? Really hey? Haven't seen that yet. Yes one TXV. I never looked at the sight glass when I was on the roof as I just opened the electrical panel.
    Monday will have to get their staff to remove product and get the back panel off to check for another motor and see if any obstruction. dont think these have another motor. then also check if evidence of a leak starting from condenser.
    Vancouver , BC
    Model of case would help.
    High side , low side pressures would help.
    More info needed.
    I'm with the other guys , with info given I would say your low on charge. Check the link JP has posted and check back with us.
    Dec 2008
    NW Iowa
    SH & SC? Sounds either low charge, or txv not feeding.