    Sporlan thermostatic element

    I have a BQ combo kit and want a thermosatic element that works for a 507 cooler. Acording to our supplier, he says go with the kt-43-sc. This, according to the sporlan bulletin, is not right and should be a kt-43-pc. He swears that others are using the sc charge. It looks to me light the freezer element sz is good for 404 and 507, but the sc cooler element is only good for 404a. Any thoughts?

  2. #2
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    You are correct: For medium temp R-507 applications you need to use the PC charge.

    If you look at the pressures for R-404A and R-507 in the medium temp range, you'll see that the 507 pressure is 4-5 lbs higher than 404A (depending on the saturation temp). There is not enough corresponding pressure developed from the original R-502 charge (which is what the SC charge is) to counteract the higher 507 pressure....hebce the PC charge was introduced for that application.

  3. #3
    Join Date
    Dec 2008
    Location
    NW Iowa
    Posts
    250
    Post Likes
    Thread Starter
    Quote Originally Posted by bunny View Post
    You are correct: For medium temp R-507 applications you need to use the PC charge.

    If you look at the pressures for R-404A and R-507 in the medium temp range, you'll see that the 507 pressure is 4-5 lbs higher than 404A (depending on the saturation temp). There is not enough corresponding pressure developed from the original R-502 charge (which is what the SC charge is) to counteract the higher 507 pressure....hebce the PC charge was introduced for that application.
    Thanks for the info.

  4. #4
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,087
    Post Likes
    also look at the box of the SC and PC and it shows the refrigerants!
    Sig removed by mod. G-Rated site

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •