    Sporlan thermostatic element

    I have a BQ combo kit and want a thermosatic element that works for a 507 cooler. Acording to our supplier, he says go with the kt-43-sc. This, according to the sporlan bulletin, is not right and should be a kt-43-pc. He swears that others are using the sc charge. It looks to me light the freezer element sz is good for 404 and 507, but the sc cooler element is only good for 404a. Any thoughts?

  2. #2
    Join Date
    May 2003
    Location
    Utah
    Posts
    733
    You are correct: For medium temp R-507 applications you need to use the PC charge.

    If you look at the pressures for R-404A and R-507 in the medium temp range, you'll see that the 507 pressure is 4-5 lbs higher than 404A (depending on the saturation temp). There is not enough corresponding pressure developed from the original R-502 charge (which is what the SC charge is) to counteract the higher 507 pressure....hebce the PC charge was introduced for that application.

  3. #3
    Join Date
    Dec 2008
    Location
    NW Iowa
    Posts
    125
    Quote Originally Posted by bunny View Post
    You are correct: For medium temp R-507 applications you need to use the PC charge.

    If you look at the pressures for R-404A and R-507 in the medium temp range, you'll see that the 507 pressure is 4-5 lbs higher than 404A (depending on the saturation temp). There is not enough corresponding pressure developed from the original R-502 charge (which is what the SC charge is) to counteract the higher 507 pressure....hebce the PC charge was introduced for that application.
    Thanks for the info.

  4. #4
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,012
    also look at the box of the SC and PC and it shows the refrigerants!
    Sig removed by mod. G-Rated site

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event