bristol dx
Hello just bought a bristol dx by hearthstone , install went good ,upon lighting did not work ,The stove now does run longer after i checked log placement ,checked pressure before valve . The stove lights and will run 3 to 5 minutes main burner shuts down and relights with pilot in continous pilot this shuts off too. This has the Sit pro falme technology ,found gas ports my manometer fittings dont fit ,I would like to check pressure before and after valve ,flame rod is in flame .Any suggestions on what other things I should work for.
-
02-02-2013, 09:54 AM #2
Regular Guest
- Join Date
- Sep 2008
- Location
- rensselaer,ny
- Posts
- 106
venting
-
02-20-2013, 11:12 PM #3
Regular Guest
- Join Date
- Sep 2008
- Location
- rensselaer,ny
- Posts
- 106
All fixed ,Found b vent on termination fitting not sealed properly ,allowing exhaust and fresh air to mix ,starving out fire ,it is running and the sit control is beeping ,warranty covering this .What do you guys use to check the gas pressure .A standard hose for a maometer will not work ,looking for 9mm inside diameter hose .Thanks
-
02-21-2013, 11:21 AM #4
If you have a B vent termination on gas direct vent, it is wrong and will need to be replaced with a direct vent termination that separates the fresh air from the exhaust. I'm hoping you're just mis-applying the nomenclature.
Are you a technician or homeowner? If not qualified, don't mess with those test ports. If qualified, you should know what equipment to use and how to do it.Keep the fire inside the fireplace.
-
02-21-2013, 06:01 PM #5
Regular Guest
- Join Date
- Sep 2008
- Location
- rensselaer,ny
- Posts
- 106
thanks this does have a direct vent kit .Working good .