txv low sh low sc
replaced a compressor #1 on a goodman package unit. M#PCB120-3. Unit has txv. After starting and running for 20 min i was getting these readings. comp#1 rla 18.6, 13.1, 13.4 , 14.3. Blwr rla 8.4, 6.2, 6.0, 5.7. CF rla 3.5 , #1,3.0,#2,2.8. pressures 52/160. S.L. temp 31. sh 3. L.L. temp 87. sc 0. amb 70. ra 73. sa 54. return air grill is clean, as is evap, blowr wheel, and cond. Motor pulley has been changed and is maxed out. im thinking txv stuck open., but wouldnt i have a higher suction pressure. txv bulb is attached properly to line. ran out of time store closed will return to finish tommorow. what do you guys think.
-
02-01-2013, 08:51 PM #2
1) how did you charge the unit? Weigh in after a deep vacuum?
2) where did you take the suction line temp?
My first thought is that you have a heat transfer issue (low suction pressure, not enough heat getting into the refrigerant). In the case of a stuck open txv, it can be a case of more refrigerant than is needed for the available heat. After all, you do have 20° across the evap.
A bad txv can be tested for by chilling and warming the bulb, and looking for changes in pressure. No change, bad txv. I'll trust that you DO know when a bulb is not correctly poitioned...
It is possible that you found what killed the compressor, too.
You did replace the dryer, right?
You have enough posts for Pro. Get that done. I don't like to put this level of detail in the open forums.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
02-01-2013, 09:15 PM #3
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
I would first verify that you have correct air flow by verifying total static pressure across the coil and confirm that it meets manufactures data specs.
What is the outside ambient temperature when taking readings.
What is return air temperature.
Do you have some form of head pressure control.
I would raise the head pressure to somewhere in the range of 200 PSIG before looking for problems. This can be accomplished many ways or as suggested by manufacture for low ambient control.
But I am still learning and looking for a new mentor.
_______________________
In a strict sense troubleshooting is not part of the repair..........understand the symptoms and you will find a solution.
-
02-01-2013, 09:32 PM #4
Professional Member
- Join Date
- Oct 2006
- Location
- tx
- Posts
- 19
I took suction temp at compressor . I did change drier . System failed acid test . I added suction drier and acid away. I pulled deep vacuum. My static pressure was 0.3 total. 0.17 supply. 0.14 return. Txv bulb placed at ten oclock. I will try warming bulb.
-
02-01-2013, 09:35 PM #5
Professional Member
- Join Date
- Oct 2006
- Location
- tx
- Posts
- 19
I weighed in charge per nameplate. I will sign up for pro membrship.
-
02-01-2013, 09:44 PM #6[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
02-01-2013, 10:05 PM #7
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
Is that a twenty ton unit with 2-ten ton compressors?
If thats the case it looks like you are not moving enough air. But you will need to cross reference with the data sheet.
What size is the duct work for the return.
What size is the supply duct.
Is this a constant volume system.
What is the space temperature which you are trying to maintain.
-
02-01-2013, 10:05 PM #8
.
OAT 70*.
Bulb @ 10 o'clock, hmmm.

..Do not attempt vast projects with
half vast experience and ideas.
...
-
02-19-2013, 09:55 PM #9
Professional Member
- Join Date
- Feb 2013
- Location
- Soon I will be in NE
- Posts
- 16
I think the airflow guys are onto something