    Nov 2009
    Boston Ma
    Siemens 600 / Apogee To Tridium Driver By CSI (3) Cubed....
    Folks, Have you ever used the Tridium Driver for the Jace By CSI Cubed....
    Have you used it with the FX60 ?
    we have a site bidding with 350 existing Siemens VAV controllers and would like to consider this product.
    Thanks in advance
    Jul 2012
    Northern NY
    not a chance. It just uses the MMI port to constantly run a monitor report that it then strips into points values. If you have ever connected to an MMI port then you know how slow this can be. It would work fine for 1 or 2 panels without many points but never to do that many panels, especially over the P2 network down to P1 level.
    I would replace each of the MBC/MEC with a JACE and use the P1 driver from InfoCon to talk directly to the VAV boxes.
    The part Number is: DR-*‐IS-*‐TEC-*‐AX-*‐J6 for a FX60 but I don't find the documents on it at the moment. You would have to call them for information.
    -Jeremy
    May 2008
    Southern CA
    Jeremy is correct, it is slow. It takes 2.5s to poll a single point.
    If you need to trend 100 points, then your poll cycle is a little over 4 minutes.
    However, if all you need are points for graphics, you could have a million points, but all you need to poll are the points being viewed.
    The more connections you add, the faster you can poll points. So if you connect to two BLN controllers (really anything with that MMI port), your poll cycle gets cut in half, and so forth. The driver also allows you to put serial to ethernet adapters on your cabinets and can tunnel over IP.