    Quote Originally Posted by LibertyTree View Post
    I'm in the pacific northwest near the coast so we don't get warm summers here. I have always sized for loss here, am I doing things incorrectly? The customer has never really used the air conditioning feature. He said maybe two or three times so its hard to get a good idea of how it works in cooling. What kind of bearing does the duct have on the output in this case?
    If your in a no A/C needed area. Then sizing for the heat load is ok. Duct work if its large enough for the 3 tons, or even large enough or 4 tons has little bearing on temp delta across the coil as long as the blower is set up for the right CFM for the heat pump size.

    A 2 stage/multi stage heat pump just slows the indoor blower when the heat pump is running in first stage. So with a 4 ton 2 stage heat pump. When its in first stage you basically have a 3 ton running on a 4 ton duct system. And still have a good temp rise.

    Get the air flow correct, and then find out why it has a poor temp delta. Could easily be that it was over charged if they had the blower speed/CFM set too high.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Mar 2002
    Posts
    520
    Post Likes
    Assuming R22 system 216psi head=>107F- 72F LLT= 35F subcooling. Overcharged?

  3. #16
    Join Date
    Feb 2012
    Location
    Waco, TX
    Posts
    3
    Post Likes
    The ductwork should not be a problem. As long as it's not too small, it will not adversely affect performance of the equipment.
    You said you weighed in the charge, so I don't think it could be overcharged enough to perform that poorly. A 15 deg temp rise assuming nominal 1200 cfm is less than 20,000 btu. I would look for a possible restriction or problem with the TXV in the outdoor unit. The suction pressure would help. I'm guessing it's low.
    I'm interested in what you find.