  1. #27
    Join Date
    Mar 2007
    Posts
    3,138
    That is good to know.
    The key to happiness is lower expectations.

  2. #28
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    314
    Quote Originally Posted by Tech Rob View Post
    It'd be great if they could come up with some new HFC low pressure refrigerant that could be used in this and the other centravacs going forward. Trane's argument against high pressure has always been "what's more environmentally friendly than a refrigerant that stays inside the chiller?" .
    Rob, if you read through back through this thread it might give you some answers, I suspect the developmental HFO refrigerant DR2 is intended for the S-series

    http://hvac-talk.com/vbb/showthread....32#post9779832
    Necessity is the mother of invention

  3. #29
    Join Date
    Mar 2007
    Posts
    3,138
    I remember that thread. I also read something about one called 1234YF. Looks like low-pressure is here to stay
    The key to happiness is lower expectations.

  4. #30
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,368
    I can't remember the name of the new refrigerant but Trane has no plans on going high pressure. A high pressure machine can't touch the efficiency of a low pressure machine. It's the laws of physics.

  5. #31
    Join Date
    Mar 2007
    Posts
    3,138
    Quote Originally Posted by R123 View Post
    I can't remember the name of the new refrigerant but Trane has no plans on going high pressure. A high pressure machine can't touch the efficiency of a low pressure machine. It's the laws of physics.
    Good point. Multi-stage, Direct drive, low pressure, semi-hermetic motor is the way to go. Also, what takes less energy; raising the pressure of a mass of vapor by 10# or by 70#?
    The key to happiness is lower expectations.

  6. #32
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,111
    Multi-stage, Direct drive, low pressure, semi-hermetic motor

    interesting thread
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  7. #33
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,132
    I seem to recall hearing somewhere about it using R145, or something like that. I had a hard time finding any numbers on whatever refrigerant it was, but it is low pressure. Slightly higher that R11, in fact I think a condensing temperature of the low 90's put it barely above 15 psig, which has me wondering if any changes will be required for the condenser vessel rating and rupture disc. And also, FWIW, this chiller is being called "Series S", whereas the older one with ceramic bearings was the "S Series". Yeah I know it's nitpicking, but we know how important correct terminology can be.

  8. #34
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,132
    After viewing that thread Screwit referenced, I believe it is R145fa.

  9. #35
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    314
    NC, I beleive you mean HFC245fa. This is one of the candidates for the replacement if HCFC123 but has physical properties where head pressure is > than 15psig/103 kPa so a coded vessel would be required.

    Commonly used in Organic Rankine Cycle systems IMHO I beleive being a HFC it may provide an interim HCFC replacement solution but longer term the low GWP of the HFO refrigerants will be the driver for selection of refrigerant low pressure chillers. Some further information attached
    Attached Files Attached Files
    Necessity is the mother of invention

  10. #36
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Quote Originally Posted by R123 View Post
    I can't remember the name of the new refrigerant but Trane has no plans on going high pressure. A high pressure machine can't touch the efficiency of a low pressure machine. It's the laws of physics.

    The important question is, when the new refrigerant comes out will you have to change you screename?

  11. #37
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    314
    Quote Originally Posted by motoguy128 View Post
    The important question is, when the new refrigerant comes out will you have to change you screename?
    Phase out not unil 2020 in new equipment and 2030 for the service tail.
    Necessity is the mother of invention

  12. #38
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,132
    Quote Originally Posted by Screwit View Post
    NC, I beleive you mean HFC245fa. This is one of the candidates for the replacement if HCFC123 but has physical properties where head pressure is > than 15psig/103 kPa so a coded vessel would be required.
    And I believe you're right about that, Screwit.

  13. #39
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,132
    Quote Originally Posted by Screwit View Post
    Commonly used in Organic Rankine Cycle systems IMHO I beleive being a HFC it may provide an interim HCFC replacement solution but longer term the low GWP of the HFO refrigerants will be the driver for selection of refrigerant low pressure chillers. Some further information attached
    Is that attachment (and you) talking about using R245fa liquid/vapor in a "steam" plant to generate electricity, as opposed to using water/steam? If so, I've never heard of such a thing. I've also never heard the term "Organic" Rankine Cycle.

Page 3 of 7 FirstFirst 1234567 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event