    Compressor flooding

    I have a walk in box, Went to job yesterday found compressor flooding. Check to make sure evap was clean and fan going right way, all good. Tried to adjust expansion valve and nothing!! Went back today put in new valve and same thing, still flooding. Is it possible my new expansion valve is bad ??? It's an old R-12 system that has 414b in it now. It seems that refrigerant is just blowing by the valve, I cant even clear the sight glass, no matter how much refrigerant I put in. Am I missing anything?

    High side pressure was about 112 and low side was about 38. Ambient temp about 64

  2. #2
    Join Date
    Apr 2010
    Location
    San Diego, CA
    Posts
    236
    Post Likes
    Sure that compressor is pumping efficiently?

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by cmclifton View Post
    Sure that compressor is pumping efficiently?
    I'm not the only one who caught that...

    How about a full set of system readings?

    Ambient temp, suction and liquid pressures and "flooding" aren't even close to enough to help you with this system.



  4. #4
    Join Date
    Aug 2000
    Location
    Phila, PA
    Posts
    259
    Post Likes
    Thread Starter
    Quote Originally Posted by cmclifton View Post
    Sure that compressor is pumping efficiently?

    If the compressor was in efficient it would be hot or at least warm, not a ball of ice, correct? I did check liquid and suction line temps, don't remeber exactly what they were, but according to pt chart I had no superheat, and about 15degrees of sub cooling if that helps. and the box will not come down in temp at all, so I basically am not getting any heat transfer across evap at all.

  5. #5
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Assuming you have the bulb in the right place and insulated well? We do need some numbers to look at. Also does this have some type of head pressure control?

  6. #6
    Join Date
    Dec 2010
    Location
    Savannah Ga.
    Posts
    54
    Post Likes
    Is there a heat exchanger mounted in the liquid/suction line? Have seen them leak internally and bleed liquid right into the suction line. Those were fun to diagnose!

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Your low side was 38 pounds which equals 47 degrees and you compressor was "a ball of ice"?


    Something is very fishy here.



  8. #8
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Did u pump down and change valve or pull charge? I'm with JP on the ice ball at 47 SST. Are you maybe grossly over charged?

  9. #9
    Join Date
    Dec 2010
    Location
    Savannah Ga.
    Posts
    54
    Post Likes
    Does the system have a heat exchanger installed?

    The more I think about this, the more convinced I am that you probably have a heat exchanger on that system and it is leaking internally, dumping liquid straight into the suction line! Has anyone else ever seen this? Anyone agree?

  10. #10
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Quote Originally Posted by icexprt View Post
    Does the system have a heat exchanger installed?

    The more I think about this, the more convinced I am that you probably have a heat exchanger on that system and it is leaking internally, dumping liquid straight into the suction line! Has anyone else ever seen this? Anyone agree?
    Yea, thru the TXV equalizer but the SH would be way low measured at the compressor and way high measured at the evap but wouldn't one visually see this while troubleshooting?

  11. #11
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Oops, you said heat exchanger. Never saw one leak internally, only externally.

  12. #12
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Ive seen an hx accumulator leak internaly, tricky one, im pretty sure there is a thread or 2 about that on here somwhere, but im horrible at finding stuff

  13. #13
    Join Date
    Aug 2000
    Location
    Phila, PA
    Posts
    259
    Post Likes
    Thread Starter
    Quote Originally Posted by jpsmith1cm View Post
    Your low side was 38 pounds which equals 47 degrees and you compressor was "a ball of ice"?


    Something is very fishy here.
    Your assuming SaT. vapor, but if I'm flooding wouldn't that be sat. liquid? then the temp is 32degrees. Now evn though I was flooding I didn't have a clear liquid line sightglass, so I did add some refrigerant to see what would happen and my pressur did increase there for so did the suction temp, but originally my suction temp was about 25 degrees when it was icing up

  14. #14
    Join Date
    Aug 2000
    Location
    Phila, PA
    Posts
    259
    Post Likes
    Thread Starter
    there is no heat exchanger and there is no external equilizer.

    Trust me I've been doing this for a long time and I'm just as confused as you guys. I know i doesn't make much sense, just looking for Ideas, because this has me stumped as of right now. I'll be back there this weekend. First thing I'm doing is taking entire charge out and re-charging to make sure charge is proper (I did a lot of adding and pulling of charge when I was there the other night) then I'll take full set of readings.

  15. #15
    Join Date
    Aug 2000
    Location
    Phila, PA
    Posts
    259
    Post Likes
    Thread Starter
    Quote Originally Posted by ryan1088 View Post
    Assuming you have the bulb in the right place and insulated well? We do need some numbers to look at. Also does this have some type of head pressure control?
    Insulated and in proper location, no head pressure control, but condensor is in a basement. the basement does get a little chilly in winter about 60degrees, but has never been a problem in past

  16. #16
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by fr420 View Post
    Your assuming SaT. vapor, but if I'm flooding wouldn't that be sat. liquid? then the temp is 32degrees. Now evn though I was flooding I didn't have a clear liquid line sightglass, so I did add some refrigerant to see what would happen and my pressur did increase there for so did the suction temp, but originally my suction temp was about 25 degrees when it was icing up

    So, you're now claiming a subcooled suction line?

    32F SCT (this is wrong, but I'll play along) with a 25 degree suction line?

    5 degrees suction subcooling?



    Your readings are wrong, friend.



    icexprt,

    I've seen suction/liquid heat exchangers blow out and leak through. Not very common to see that particular part on smaller equipment like this.



  17. #17
    Join Date
    Aug 2000
    Location
    Phila, PA
    Posts
    259
    Post Likes
    Thread Starter
    Quote Originally Posted by jpsmith1cm View Post
    So, you're now claiming a subcooled suction line?

    32F SCT (this is wrong, but I'll play along) with a 25 degree suction line?

    5 degrees suction subcooling?



    Your readings are wrong, friend.



    icexprt,

    I've seen suction/liquid heat exchangers blow out and leak through. Not very common to see that particular part on smaller equipment like this.
    I dont know if you mis-understood me or your just an arrogant prick. But never once claimed I had a subcooled suction line. I said temp was originally 25 and rose to 32degrees as I added some refigerant.

  18. #18
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Is the box full of turkey ice cream and is your name Feng?


    Did you do a pumpdown test and check amps vs nameplate? Also, I know I've seen somewhere 414b do not to charge by sight glass.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  19. #19
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by fr420 View Post
    I dont know if you mis-understood me or your just an arrogant prick. But never once claimed I had a subcooled suction line. I said temp was originally 25 and rose to 32degrees as I added some refigerant.

    You said that you measured a 38 pound suction line with 414b, then disagreed with me when I pointed out that it was impossible for ice to form at that condition. (47 degrees Saturation Temp)


    You said that you thought that you should use the bubble point (liquid side) for the suction line (32 Saturation temp). This is incorrect, you would use DEW point for the suction side of the system.

    So, I'm using what you've given me of your readings and some simple math to point out why I think that your readings are erroneous.

    You can call me an arrogant prick if you like, I've been called worse and I'm still standing.

    What I do know is refrigeration, and something here isn't adding up.



  20. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    icexprt,

    I've seen suction/liquid heat exchangers blow out and leak through. Not very common to see that particular part on smaller equipment like this.
    I've seen a number of them over the years, only on R12 systems
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •