 Originally Posted by fr420
I understand exactly what your saying, but the condition I was having The dew point reading would give me a subcooled suction line, and the bubble point reading was only one that made sense because as we know now I was coming back straight liquid.
Follow what is actually happening with the dew point/bubble point.
The area between the two is the saturation area of the refrigerant and liquid can exist at any point between the two.
-
Glad you got it solved! The first one we saw took us several trips over a couple of days to figure out also! I guarantee you'll never forget about it and if you ever see it again you'll go right to the problem!