there is no heat exchanger and there is no external equilizer.
Trust me I've been doing this for a long time and I'm just as confused as you guys. I know i doesn't make much sense, just looking for Ideas, because this has me stumped as of right now. I'll be back there this weekend. First thing I'm doing is taking entire charge out and re-charging to make sure charge is proper (I did a lot of adding and pulling of charge when I was there the other night) then I'll take full set of readings.
-
02-01-2013, 08:45 PM #15
Professional Member
- Join Date
- Aug 2000
- Location
- Phila, PA
- Posts
- 131
-
02-01-2013, 09:13 PM #16
So, you're now claiming a subcooled suction line?
32F SCT (this is wrong, but I'll play along) with a 25 degree suction line?
5 degrees suction subcooling?
Your readings are wrong, friend.
icexprt,
I've seen suction/liquid heat exchangers blow out and leak through. Not very common to see that particular part on smaller equipment like this.
-
02-01-2013, 09:35 PM #17
Professional Member
- Join Date
- Aug 2000
- Location
- Phila, PA
- Posts
- 131
-
02-01-2013, 09:47 PM #18
Is the box full of turkey ice cream and is your name Feng?

Did you do a pumpdown test and check amps vs nameplate? Also, I know I've seen somewhere 414b do not to charge by sight glass.Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
02-01-2013, 09:51 PM #19
You said that you measured a 38 pound suction line with 414b, then disagreed with me when I pointed out that it was impossible for ice to form at that condition. (47 degrees Saturation Temp)
You said that you thought that you should use the bubble point (liquid side) for the suction line (32 Saturation temp). This is incorrect, you would use DEW point for the suction side of the system.
So, I'm using what you've given me of your readings and some simple math to point out why I think that your readings are erroneous.
You can call me an arrogant prick if you like, I've been called worse and I'm still standing.
What I do know is refrigeration, and something here isn't adding up.
-
02-01-2013, 09:52 PM #20
-
02-01-2013, 09:56 PM #21
Easy big fella. Your numbers are confusing. You said originally 25 degree suction with 38psi. That would indicate a sub cooled condition. Even if you added refrigerant and raised the suction to 32 the SST is 44+ so something isn't adding up. Maybe we are talking about different things. When you say suction temp are you talking about saturated suction temp, from your PT chart, or the actual suction temp, taken with a thermometer?
-
02-01-2013, 09:59 PM #22
Given that 414b is a blend, what you're describing is THEORETICALLY possible, though.
If that is the case, you're dumping almost PURE liquid into that compressor and it's probably already dead.
Time to start at the beginning and find out WHY you aren't absorbing enough heat in the evaporator to fully boil all of the refrigerant being fed by the TEV.
Dirty? Fans? Oversized valve? Valve stuck open?
-
02-01-2013, 10:00 PM #23
-
02-01-2013, 10:06 PM #24
Professional Member
- Join Date
- Aug 2000
- Location
- Phila, PA
- Posts
- 131
-
02-01-2013, 10:11 PM #25
Without proper readings everyone is making guesses
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
02-01-2013, 10:21 PM #26