    Compressor flooding
    I have a walk in box, Went to job yesterday found compressor flooding. Check to make sure evap was clean and fan going right way, all good. Tried to adjust expansion valve and nothing!! Went back today put in new valve and same thing, still flooding. Is it possible my new expansion valve is bad ??? It's an old R-12 system that has 414b in it now. It seems that refrigerant is just blowing by the valve, I cant even clear the sight glass, no matter how much refrigerant I put in. Am I missing anything?
    High side pressure was about 112 and low side was about 38. Ambient temp about 64
    Apr 2010
    San Diego, CA
    Sure that compressor is pumping efficiently?
    Quote Originally Posted by cmclifton View Post
    I'm not the only one who caught that...
    How about a full set of system readings?
    Ambient temp, suction and liquid pressures and "flooding" aren't even close to enough to help you with this system.
    Aug 2000
    Phila, PA
    If the compressor was in efficient it would be hot or at least warm, not a ball of ice, correct? I did check liquid and suction line temps, don't remeber exactly what they were, but according to pt chart I had no superheat, and about 15degrees of sub cooling if that helps. and the box will not come down in temp at all, so I basically am not getting any heat transfer across evap at all.
    Mar 2009
    Mid-Mo
    Assuming you have the bulb in the right place and insulated well? We do need some numbers to look at. Also does this have some type of head pressure control?
    Dec 2010
    Savannah Ga.
    Is there a heat exchanger mounted in the liquid/suction line? Have seen them leak internally and bleed liquid right into the suction line. Those were fun to diagnose!
    Your low side was 38 pounds which equals 47 degrees and you compressor was "a ball of ice"?
    Something is very fishy here.
    Jul 2012
    Western KY
    Did u pump down and change valve or pull charge? I'm with JP on the ice ball at 47 SST. Are you maybe grossly over charged?
    Dec 2010
    Savannah Ga.
    Does the system have a heat exchanger installed?
    The more I think about this, the more convinced I am that you probably have a heat exchanger on that system and it is leaking internally, dumping liquid straight into the suction line! Has anyone else ever seen this? Anyone agree?
    Jul 2011
    Lehigh Valley, PA
    Quote Originally Posted by icexprt View Post
    Yea, thru the TXV equalizer but the SH would be way low measured at the compressor and way high measured at the evap but wouldn't one visually see this while troubleshooting?
    Jul 2011
    Lehigh Valley, PA
    Oops, you said heat exchanger. Never saw one leak internally, only externally.
    Oct 2005
    B.C. Canada
    Ive seen an hx accumulator leak internaly, tricky one, im pretty sure there is a thread or 2 about that on here somwhere, but im horrible at finding stuff
    Aug 2000
    Phila, PA
    Your assuming SaT. vapor, but if I'm flooding wouldn't that be sat. liquid? then the temp is 32degrees. Now evn though I was flooding I didn't have a clear liquid line sightglass, so I did add some refrigerant to see what would happen and my pressur did increase there for so did the suction temp, but originally my suction temp was about 25 degrees when it was icing up