Results 1 to 5 of 5
    Jun 2006
    New Jersey
    Integrating Some TAC/Invensys Actuators
    I have a few AHU's with MP-5413 actuators on the HW and CHW. Doing some research and they are stated at 2-15vdc. I only have 0-10vdc. So I was looking into some dc to dc transmitters. Then I came across some info, that the actuators only stroke from 6-9vdc.
    What's the deal?
    Click image for larger version.
    Hampton Roads, Virginia
    Here a datasheet 3v operating range anywhere between 2-15
    Kevin
    Attached Images Attached Images
    "Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."
    James Rouse
    Jun 2006
    New Jersey
    Thanks for the info.
    So do I understand this right......the range is 3vdc. The starting point(approximate) is 6vdc.....but is fixed. But also states, that the starting point is adjustable. And requires 2-15vdc.
    Now I'm even more confused.
    May 2009
    in the present
    Maybe something like this would help http://workaci.com/products/arm-anal...scaling-module
    Jun 2006
    New Jersey
    I threw a commissioning tool on a valve today. It does only seem to stroke between about 6-9vdc.
    I also monitored the existing controllers that are controlling the Ahu's. They were feeding 4vdc at 0% and 9vdc at 100%. The system is a old Tracer 100.
    So I'm just going to set up my new controllers at 6-9vdc.