Results 1 to 5 of 5
  1. #1
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,383
    Post Likes

    Integrating Some TAC/Invensys Actuators

    I have a few AHU's with MP-5413 actuators on the HW and CHW. Doing some research and they are stated at 2-15vdc. I only have 0-10vdc. So I was looking into some dc to dc transmitters. Then I came across some info, that the actuators only stroke from 6-9vdc.

    What's the deal?

    Name:  0fbbcb36-4403-4c00-882a-b67c29124f58.jpg
Views: 117
Size:  35.8 KB

  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,855
    Post Likes
    Here a datasheet 3v operating range anywhere between 2-15


    Kevin
    Attached Images Attached Images
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria

    "It's not the customer's job to know what they want." -- Steve Jobs

  3. #3
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,383
    Post Likes
    Thread Starter
    Thanks for the info.

    So do I understand this right......the range is 3vdc. The starting point(approximate) is 6vdc.....but is fixed. But also states, that the starting point is adjustable. And requires 2-15vdc.

    Now I'm even more confused.

  4. #4
    Join Date
    May 2009
    Location
    in the present
    Posts
    94
    Post Likes
    Maybe something like this would help http://workaci.com/products/arm-anal...scaling-module

  5. #5
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,383
    Post Likes
    Thread Starter
    I threw a commissioning tool on a valve today. It does only seem to stroke between about 6-9vdc.

    I also monitored the existing controllers that are controlling the Ahu's. They were feeding 4vdc at 0% and 9vdc at 100%. The system is a old Tracer 100.

    So I'm just going to set up my new controllers at 6-9vdc.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.