    Water Treatment...

    Let's talk about water treatment. I'm not sure if chemical less water treatment is practical. And the costs of the equipment are expensive but supposedly will pay for it's self in the long run.

    I live in the Desert southwest, our water is hard but we have softened water to the towers. We use (2) different methods of water treatment.

    One method we use utilizes sulfuric acid and a seperate inhibitor. We maintain a ph of 7.2 and 7.4. and a conductivity of 3600.

    Our other method is maintaining conductivity of 2500 and using an inhibitor. Both methods are a "bleed then feed" approach.

    At one of our buildings I have a Griswold skid mounted tower filter system. It has a centrifugal seperator and a bag filter. It has a pump of it's own which drafts off the side of a 6" condenser water line. This system is worth it's weight in gold. I clean out lots of "silt" and other fine debris from the bag filter. I understand this is not a realistic form of water treatment but it is a tremendous help.

    Griswold also has a chemical less water treatment method called SBC Scale Bacteria Corrosion. Has anyone used this or any other methods of chemical less water treatment programs?
    Quick reply to this message Reply  

  2. #2
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,664
    Post Likes

    Post Eddy Current and the Magnetic Fields...Now Playing...

    Two of the centrifugals I service are on a Dolphin system.

    It kinda sorta works, but you need to be able to remove the solids that will drop out in places including the tubes. It will work better in towers with a V shape along with a cyclonic separator. With flat bottomed towers you would need to suck out the gunk or install the cyclonic separator and a pump with some spray trees in the tower to kick up the solids and get them out. I'd lean away from sand filters. Bags might work if you cleaned them a lot.

    There are other concerns such as white rust in a new system, and how well it deals with the sulphate reducing bacteria like the bugs that make the blisters with bright metal underneath.

    So far we have to clean the tubes every year, and the pay off compared to our standard phosphonate based tower treatment with a Bromine biocide pencils out to far beyond the expected life of the unit.

    The guy who invented the thing now works for Evapco, and they have their own version.

    If they get it to work and pencil out, the green frenzy will beat a path to their door. At this time, however, I could neither recommend or condemn the Dolphin.
    God Bless our Veterans

    God Bless the USA
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Post Likes
    You say your water is hard. How hard. In San Jose I always advise people to chew the water before swallowing. But is is better to treat. Our total disolved solids on raw water runs from 500 to 700 miro mos.

    Now my brother works in the Salinas Valley. The raw runs over 1700. He has found it cheaper to replace the condenceers every two years than buy the chemicals. It is a NH3 plant.

    So haw hard is you water?
    Old snipes don't die they just loose their steam
    Quick reply to this message Reply  

  4. #4
    Join Date
    Sep 2007
    Location
    Yuma, Arizona
    Posts
    252
    Post Likes
    Thread Starter
    City water around here is about 1400.

    The Griswold filtration system I have incorporates a basin sweeper which helps stir it up a little. I'd really like to try out the SBC from Griswold but I'd hate to piss the money away if it does not do what it says it can do. Perhaps I'll contact them and see it they can give a written guarantee on what they say it will accomplish?

    What kind of towers are you using and what type of application are you using these towers on that your replacing them every two years? Are you using any stainless towers?

    At one of our buildings I have a TowerTech cooling tower. It's all fiberglass and plastic. It sucks because they did not design it with servicing it in mind. It's a unique design which does not allow you to access the basin. Luckily it's getting scrapped this winter.
    Quick reply to this message Reply  

  5. #5
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Post Likes
    I believe he has Evaporative towers with NH3 used in food processing. I have not seen the plant. He has tried several different companies, but the cost of chemicals was more than new condencerss.
    Old snipes don't die they just loose their steam
    Quick reply to this message Reply  

  6. #6
    Join Date
    Aug 2007
    Posts
    19
    Post Likes
    Can't beat chemicals.

    Where I work, they use Nalco, they use a biocide, and an inhibitor. (3D Trasar?)and maintain a 1800 conductivity, 8 cycles of conductivity. In the off season, a petroleum based lay up chemical (northeast here.)

    Some towers use a Vortisand self backwashing sand filter, or a side stream pleated filter element.

    The Dolphin was on a trial period on one of the towers. Can't prove it worked, or that it didn't work, for the amount of time it was in the system, but the make up water use went up considerably, they said no thanks and gave it back.

    Hope this helps, I'm not versed in water treatment, but I hope this helps somewhat!
    Quick reply to this message Reply  

  7. #7
    Join Date
    Sep 2005
    Location
    Cincinnati, OH
    Posts
    27
    Post Likes

    Smile Chemical Free Systems & Air Intake Filter Screens

    Here's a chemical free water treatment system that is worth checking out - it's called the VRTX system - the way it works is that water is drawn from the Cooling Tower or Evaporative Condenser sump. The water is spun at high velocity in apposing directions then the two streams collide with tremendous kinetic energy and shear. At the core of these streams, a region of near total vacuum is created which degasses the flow; Under these conditions, hydrodynamic cavitation occurs causing intense temperatures (up to 9,000°F) (kinda like colliding atoms together) - Simply stated it causes debris to become emulsified.

    However, no matter how well the chemical free technology works there are still drawbacks such as they do nothing to manage airborne debris that gets into the fill nor do they solve the problem with algae which grows in the interior regions of the tower exposed to sunlight. Another thought when trying to help customers solve their water quality problems is to keep in mind that 90% of the bio-loading is caused by airborne debris pulled into the intake opening and that using chemical free water treatment and side stream filtration only manages the debris after it gets into the tower. An important part of managing water quality is managing the airborne debris which gets into the tower - Use of air intake filter screens will stop most airborne matter from getting into the cooling tower thus enabling either chemical or chemical free water treatment systems to perform more effectively. Also, because air intake filter screens shade the tower it thwarts the photosynthesis process by difusing the sunlight which algae needs as its energy source for growth - when air intake filters are used in conjunction with chemical water treatment, it also enables the reduction in bromine solutions frequently used to help manage tough algae problems. In short, air intake filter screens can help stop airborne debris from getting into the systems in the first place thus increasing the effectiveness of water treatment systems through the significant reduction in bio-loading. If however the primary problem is water borne debris, then filter screens can't help and it's up to chemistry, or chemical free systems and side stream filters to solve the problem.
    Last edited by randysimmons; 11-20-2007 at 08:55 PM. Reason: Additional Point
    Quick reply to this message Reply  

  8. #8
    Join Date
    Dec 2004
    Location
    Mid-west
    Posts
    567
    Post Likes
    There have been may discussions about the Dolphin systems almost 100% say they're junk. I have seen many types of systems, the side cyclone type help remove solids work good, but chemicals help every system I've worked on. When replacing the condensers is cheaper than chemicals I wonder if higher electrical usage and additional wear on the equipment is figured in, additional maintenance, oil changes, higher pressures all should be included. Its never been my experience that this is a good trade off for chemicals.
    Quick reply to this message Reply  

  9. #9
    Join Date
    Mar 2008
    Location
    Louisville, KY
    Posts
    16
    Post Likes
    I've sold EVAPCO's Pulse-Pure system on several of their units all have worked great in my area, but the water is totally different in yours. The Pulse Pure is at a generation 7 while the Dolphin has not improved at all. The reason a lot of the Dolphin systems do not work is because they do not run water analysis first. While the Dolphin and Pulse-Pure operate on similar technology EVAPCO recognizes that it will only operate effeciently if the water sample is approved. I have a friend in Arizona and it is really spotty if that system will work or not.

    One easy thing you can do is contact the local EVAPCO rep and send him a 16 oz water sample and he can tell you whether or not it is applicable. It shouldn't cost anything to have the sample run. Check out the link below if anyone is interested.

    http://www.evapco.com/pulse-video.asp
    Quick reply to this message Reply  

  10. #10
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    We work on a number of large packaged rooftop that utilize evap condensers and also the fishie (dolphin) water treatment systems. So far they seem to work. As stated though the cause the particulate to drop out of suspension in the tower sump. This requires the basins of the towers to be cleaned once or twice per season.
    Quick reply to this message Reply  

  11. #11
    Join Date
    Sep 2009
    Posts
    13
    Post Likes
    I don't see a lot of talk on this anywhere else and am new to the board. Has their been any changes in thinking with this alternative technology? I hate to revive such an old thread but this is what the search revealed and I am looking for some input.
    Quick reply to this message Reply  

  12. #12
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,664
    Post Likes
    Before you invest, be sure it pays for itself within the expected lifespan of the unit.

    I'm not so sure the Dolphin does. For the price, you can buy a lot of chemicals, pumps and controllers. And we have real good water here.

    From what I've seen of Evapco's system, it might have a better chance of working for you. But listen to what they have to say about your water and the chances for success.
    God Bless our Veterans

    God Bless the USA
    Quick reply to this message Reply  

  13. #13
    Join Date
    Sep 2009
    Posts
    13
    Post Likes
    Quote Originally Posted by Randy S. View Post
    Before you invest, be sure it pays for itself within the expected lifespan of the unit.

    I'm not so sure the Dolphin does. For the price, you can buy a lot of chemicals, pumps and controllers. And we have real good water here.

    From what I've seen of Evapco's system, it might have a better chance of working for you. But listen to what they have to say about your water and the chances for success.
    Thanks Randy.

    I have researched them both as well as one other and they seem to each have their pros and cons. I am looking for the simplest alternative and I am a bit concerned about the installation process and short warranty.

    Chemicals are not getting cheaper, neither is water, neither are the pumps and controls for that matter. Something has to surface that can stand up to the chemical lobby and provide a solution.

    That is my hope anyway.
    Quick reply to this message Reply  

  14. #14
    Join Date
    Mar 2003
    Location
    Cincinnati
    Posts
    7,977
    Post Likes
    I allowed our water treatment company to use one of my towers as a trial for a system called uvox. It utilizes a uv light on a sidestream set-up. It has been in place all summer, we've used no chemicals and the tower water is so clean you would be tempted to drink it. I ran several dip slide tests on it and only one red dot grew each time. I was skeptical but so far I am very impressed.
    Quick reply to this message Reply  

  15. #15
    Join Date
    Sep 2009
    Posts
    13
    Post Likes
    Quote Originally Posted by mattm View Post
    I allowed our water treatment company to use one of my towers as a trial for a system called uvox. It utilizes a uv light on a sidestream set-up. It has been in place all summer, we've used no chemicals and the tower water is so clean you would be tempted to drink it. I ran several dip slide tests on it and only one red dot grew each time. I was skeptical but so far I am very impressed.

    anything more specific? what is the payback for your system and how large is your system?
    Quick reply to this message Reply  

  16. #16
    Join Date
    Oct 2009
    Posts
    8
    Post Likes
    While I was browsing, I happened to find this site. I am a regional manager for Griswold Water Systems. We manufacture the SBC. It is similar to the Dolphin in concept (the Pulse-Pure is a reverse engineered Dolphin unit), however our implementation and approach is unique. If you want a competitive comparison see our website or email me (rob at griswoldwatersystems dot com).

    The reason that I am joining the conversation is to answer some of the questions that were posted.

    1. Basin Cleaning – Pulse-Power based systems like the SBC, Dolphin, and Pulse-Pure cause calcium and other debris to flocculate out into the basin because that is where the water flows the slowest. As long as the flow everywhere else is 2ft/sec or more, the precipitant will stay suspended in the water. Use sweeper piping when possible or you may have to clean out the basin a little more frequently than you did before. Do NOT use a poor sweeper design because it will just make it harder to clean the basin. We design our own sweeper systems after seeing so many poorly designed systems in the field. Evapco (who is also a competitor) seems to do a better job with their sweeper designs than Marley and BAC, but any tower can have an effective sweeper system. The question is, is the tower large enough to merit a sweeper system?
    Quick reply to this message Reply  

  17. #17
    Join Date
    Oct 2009
    Posts
    8
    Post Likes
    2. Payback – I have some return on investment tools that usually show a payback of 6 months to 24 months. There are too many factors for me to list right now, but with our system, the payback is there and usually it is pretty quick.
    3. Throwing away money – We will REFUND your money if we cannot get it to work in 90 days. No risk!
    4. Chemicals work – That is true. However, I have seen very few towers that have been treated by chemicals and have never had a single problem. Often, chemical water treaters get replaced because the owner does not think they are doing a good job. This may be due to a number of reasons (water source changed, operation changed, chemical ran out, valve stuck open or closed, poor service, unable to keep bacteria counts low…) With all of this in mind, chemicals usually work if tended very closely, but there are some places where chemicals just can’t seem to do the job. It goes both ways though. Sometimes our unit (and our competitors’ units) need corrosion inhibitor.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Oct 2009
    Posts
    8
    Post Likes
    5. Hard water – Our hardware works great in hard water. If the water is too hard, it may simply limit the cycles of concentration, but it should still be better than chemicals.
    6. Make up water – We (not our competitors) almost always cycle the water higher than with chemicals. This means that you will lose LESS water with our system than you would with chemicals. Dolphin is hit and miss here (from my experience). Evapco does a limited analysis (better). We do a comprehensive analysis before determining the conductivity setpoint for the blowdown. Evapco walks away from a lot of jobs where we succeed, because they do not like the quality of the water. We will tell you up front if we may need some corrosion inhibitor instead of walking away from the job.
    7. VRTX – Feel free to look at it, but I think that you will see that it is not a major competitor for many reasons. I do not need to elaborate. Email me if you want more details (rob at griswoldwatersystems dot com).
    8. Dolphin – They actually work many times, but the implementation and maintenance is usually what kills them.
    Quick reply to this message Reply  

  19. #19
    Join Date
    Oct 2009
    Posts
    8
    Post Likes
    9. Water samples – We also require a water sample before we installing our SBC. Good that Evapco is on the right path here. We also do not charge for this service.
    10. Change in non-chemical thinking – Yes, there has been a recent change in the industry. I have met with many engineering firms that will ONLY specify non-chemical water treatment. This is more the case along the west and east coasts than inland.
    11. Simplest approach – We make filtration and treatment hardware and package it together for simple installation and implementation. Our SBC unit only requires 110/120 power and draws less than 80 watts. No one else can touch that!
    12. Low bacteria counts – I have seen reports of 20 CFU/ML (drinking water is 500CFU/ML), but 1,000CFU/ML is common.
    Quick reply to this message Reply  

  20. #20
    Join Date
    Oct 2009
    Posts
    8
    Post Likes
    I hope that information helps. Please let me know if you have any more questions.
    Quick reply to this message Reply  

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •