Thread: Tracer SC question
-
01-30-2013, 08:08 PM #1
Tracer SC question
I have 4 reliatel RTU units ( packaged gas heat , cooling , etc ) that have Tracer SC controllers ( comm4? ). The control system is not online but they are asking me to start the units for temp. heat. Can I just connect a zone sensor and or do I need to disconnect the comm board from the reliatel ? Replies appreciated.
-
01-30-2013, 08:31 PM #2
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 297
If Tracer Summit is not in control as a first priority than the unit will look for another means for secondary control. Why don't you just simply install a conventional thermostat. It will work just fine that way.
-
01-30-2013, 08:35 PM #3
Cool , I wasn't sure if the unit would just sit there if there was no communication. Thanks very much.
-
05-16-2013, 10:11 PM #4
New Guest
- Join Date
- May 2011
- Posts
- 3
Hi!, I remember reliatel RTU is using COMM4. But Tracer SC don't have COMM4. It using COMM5, BACnet MSTP/IP only.
-
05-19-2013, 10:16 AM #5
-
05-19-2013, 09:56 PM #6
New Guest
- Join Date
- May 2011
- Posts
- 3
Hi!,
We no need BCU as gateway for SC. The BCI-R is gateway if you want intergrated beetwen Reliatel RTU and Tracer SC.