Page 1 of 2 12 LastLast
Results 1 to 13 of 15
  1. #1
    Join Date
    Nov 2009
    Location
    Boston Ma
    Posts
    23
    Post Likes

    Siemens 600 / Apogee To Tridium Driver By CSI (3) Cubed....

    Folks, Have you ever used the Tridium Driver for the Jace By CSI Cubed....
    Have you used it with the FX60 ?
    we have a site bidding with 350 existing Siemens VAV controllers and would like to consider this product.
    Thanks in advance

  2. #2
    Join Date
    Jul 2012
    Location
    Northern NY
    Posts
    121
    Post Likes
    not a chance. It just uses the MMI port to constantly run a monitor report that it then strips into points values. If you have ever connected to an MMI port then you know how slow this can be. It would work fine for 1 or 2 panels without many points but never to do that many panels, especially over the P2 network down to P1 level.

    I would replace each of the MBC/MEC with a JACE and use the P1 driver from InfoCon to talk directly to the VAV boxes.

    The part Number is: DR-*‐IS-*‐TEC-*‐AX-*‐J6 for a FX60 but I don't find the documents on it at the moment. You would have to call them for information.

    -Jeremy

  3. #3
    Join Date
    May 2008
    Location
    Southern CA
    Posts
    66
    Post Likes
    Jeremy is correct, it is slow. It takes 2.5s to poll a single point.

    If you need to trend 100 points, then your poll cycle is a little over 4 minutes.

    However, if all you need are points for graphics, you could have a million points, but all you need to poll are the points being viewed.

    The more connections you add, the faster you can poll points. So if you connect to two BLN controllers (really anything with that MMI port), your poll cycle gets cut in half, and so forth. The driver also allows you to put serial to ethernet adapters on your cabinets and can tunnel over IP.

    The driver has been around for quite some time, is proven and stable. You just need to be a little smarter about how you use it.

  4. #4
    Join Date
    Feb 2008
    Posts
    10
    Post Likes
    Quote Originally Posted by BostonCtls View Post
    Folks, Have you ever used the Tridium Driver for the Jace By CSI Cubed....
    I have a CSI3 3.6.47.1 running on a Jace7. The driver is able to Discover controllers on the network as well as the point data in the controllers.
    My installation is talking to 2 Sys600 MEC Cabinets. 1 is pulling 18 points (read only), and the other is pulling 2 read only points and 1 writable point (a temperature). My read only points seem to work like a champ, but the writable one freezes up after a couple of days and stops responding to changes. Sometimes reattaching the link will get it going again, but more often than not, I have to delete the point and re-discover it. I thought it was a speed thing even though my message queue is at 0, so I changed it to only send changes once every 5 min. and still have problems.

  5. #5
    Join Date
    Sep 2012
    Posts
    5
    Post Likes
    I'm looking at putting a JACE on an Apogee system - any chance we could email directly? I'd like to cut to the chase on this one, and could use some input.
    Thanks in advance.

  6. #6
    Join Date
    Sep 2007
    Posts
    272
    Post Likes
    I've done it, not conventionally though as to all jace driver options would not work. We had the customer purchase insight BACnet server and we made the insight server a glorified bacnet router.


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Sep 2007
    Posts
    272
    Post Likes
    Dadof5
    My email is in my profile, email me with questions.



    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Apr 2014
    Location
    Minneapolis, MN
    Posts
    9
    Post Likes
    Can you get any points out of the MEC controllers at all?

  9. #9
    Join Date
    Sep 2007
    Posts
    272
    Post Likes
    Yes it communicates through the mmi port, it is very slow.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Mar 2015
    Posts
    15
    Post Likes
    I have a job where there's a Siemens' Trunk Interface II communicating to multiple MBC's. Does the JACE's RS-232 connect to the RS-232 on the Trunk Interface II? Specifically, how does the JACE connect to the MBC's? The MBC's are already networked, I'm assuming I need to break the connection from the Trunk Interface II and go directly into the JACE, but how?

  11. #11
    Join Date
    Sep 2007
    Posts
    272
    Post Likes
    No, you can not hook up the trunk interface to the jace, your only options are to use the csi driver thu the mmi port or if the insight server has a bacnet license, you can export the points via bacnet ip.

    Sent from my SM-G900V using Tapatalk

  12. #12
    Join Date
    Mar 2015
    Posts
    15
    Post Likes
    Quote Originally Posted by WillyTech View Post
    No, you can not hook up the trunk interface to the jace, your only options are to use the csi driver thu the mmi port or if the insight server has a bacnet license, you can export the points via bacnet ip.

    Sent from my SM-G900V using Tapatalk
    If I have multiple Siemens' MBC panels, do I need to hook up just one to see all of them? Or do I need a separate JACE per MBC? The latter will be astronomically high if I have multiple MBCs.

  13. #13
    Join Date
    Sep 2007
    Posts
    272
    Post Likes
    You only need to hook up to one panel on a single P2 network. Huge downside to that is the more points you have in point monitor the slower this solution will be. Your expectation shouldn't be to high as a replacement to the insight front end.

    Sent from my SM-G900V using Tapatalk

Page 1 of 2 12 LastLast