    883060 true t-stat instructions needed

    i ordered a t-state for a old true 2 door freezer
    i came with a relay and some new wiring, and no instructions..
    true is closed

    anyone got these instal instructions?

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,748
    If there is a Grasslin clock in the unit you need the relay. If it's a Paragon you don't. The relay was added because the inrush of current was causing the contacts on the Grasslin timers to weld. Someone here might have a wiring diagram. Wish I could be more help The relay would be located in the chase the compressor pugs into
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  3. #3
    Join Date
    May 2005
    Posts
    1,225
    it has a regular 8141-00 timer..so i can just replace the t-stat then??

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,748
    Yes.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  5. #5
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,753
    Here's a link in the Educational Forums for the 2007 True Service Manual which has a section on temperature controls which covers those relays:

    http://hvac-talk.com/vbb/showthread....-Manufacturing

    If the new thermostat is a Danfoss and the compressor is larger than a 1/3 hp, you will need the relay.

  6. #6
    Join Date
    May 2005
    Posts
    1,225
    wow, thanks icemeister..