01-29-2013, 07:15 PM #1
883060 true t-stat instructions needed
i ordered a t-state for a old true 2 door freezer
i came with a relay and some new wiring, and no instructions..
true is closed
anyone got these instal instructions?
-
01-29-2013, 07:34 PM #2
If there is a Grasslin clock in the unit you need the relay. If it's a Paragon you don't. The relay was added because the inrush of current was causing the contacts on the Grasslin timers to weld. Someone here might have a wiring diagram. Wish I could be more help The relay would be located in the chase the compressor pugs into
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-29-2013, 08:00 PM #3
it has a regular 8141-00 timer..so i can just replace the t-stat then??
-
01-29-2013, 09:02 PM #4
Here's a link in the Educational Forums for the 2007 True Service Manual which has a section on temperature controls which covers those relays:
http://hvac-talk.com/vbb/showthread....-Manufacturing
If the new thermostat is a Danfoss and the compressor is larger than a 1/3 hp, you will need the relay.
-
01-29-2013, 08:53 PM #5
Yes.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-29-2013, 11:11 PM #6
wow, thanks icemeister..