Page 1 of 9 12345678 ... LastLast
Results 1 to 13 of 107
    Jan 2013
    San Gabriel Valley, California
    Cool FengsHVAC a Professional HVAC Tech teach you how to fix the heat on Bryant Pkg Unit
    Problem: heat pump produce no heat, only blow cold air.
    Insight: Called for heat, Blower ran, but compressor didn't come on.
    Cause: dirty air filter cause the high pressure switch to trip during heat mode.
    Solution: While it was calling for heat, checked 24v on the Y wire from the thermostat at the unit, got 24v. checked 24v at the compressor contactor coil, no voltage. found High pressure swith is in between, reset it. cleaned the air filter, turned the heat back on.
Size:  59.5 KBName:  64685_106780512832688_1333545451_n.jpg
Size:  39.7 KBName:  230667_106780762832663_134531897_n.jpg
    Nov 2011
    St. Louis
    Teach us more, all knowing and wise Fengmaster...
    Was the reversing valve energized while you had 24v at Y?
    Feb 2012
    EVERYWHERE
    And now it's time for HVAC talk with FengsHVAC.
    Jan 2013
    Bryant unit use O ternimal for the reversing valve, which means that reversing valve is energize in Cooling Mode. During Heating Mode Reversing Valve is de-energized... so , While i had 24v at Y, i didn't get any power at the reversing valve on heating mode..
    butler pa
    wow...heat pump class
    Southeastern Pa
    Check the filter class.....
    2 Tim 3:16-17
    AOP Forum Rules:
    You better fix that refer leak below the HPS.
    change a filter, Fix a heat pump.
    Mar 2009
    Mid-Mo
    I long to be as technically proficient as the OP.
    May 2012
    Upper Michigan
    If you work hard enuf all of your dreams will come true!
    Work smarter and all your dreams will come true.
    fake it 'til you make it
    Oct 2011
    Chicagoland Area
    Quit working and suck off the governments teat and you're set for life
