Results 1 to 2 of 2
  1. #1
    Join Date
    Oct 2014
    Location
    Rutland Vt
    Posts
    1
    Post Likes

    Mistsubishi Mini Split Comm Error Off Grid

    Hi Guys, Dan here. We just installed an Outback 8kW VFX7248 fully off grid system for a client who also purchased and installed three Mitsubishi mini split heat pumps. The Power System is performing flawlessly. The heating systems.. not so much. The customer can light up each unit individually, but when she attempts to light up more than one, the each consecutive unit trips out on comm error. If she shuts down everything (From the breaker box) she gets the same results starting from which ever unit she first started. The HVAC guys would love to blame the solar guys (as would the lawn care guys), All my guys blame the HVAC guys. I've heard of adding caps to the 240vac input, but each unit is on its own circuit, there should not be Power Factor/ harmonic distortion issue. I'm blaming bad Sushi. Advise? Thanks db

  2. #2
    Join Date
    May 2011
    Location
    Ottawa Ontario
    Posts
    13
    Post Likes
    Quote Originally Posted by Foxfire Energy View Post
    Hi Guys, Dan here. We just installed an Outback 8kW VFX7248 fully off grid system for a client who also purchased and installed three Mitsubishi mini split heat pumps. The Power System is performing flawlessly. The heating systems.. not so much. The customer can light up each unit individually, but when she attempts to light up more than one, the each consecutive unit trips out on comm error. If she shuts down everything (From the breaker box) she gets the same results starting from which ever unit she first started. The HVAC guys would love to blame the solar guys (as would the lawn care guys), All my guys blame the HVAC guys. I've heard of adding caps to the 240vac input, but each unit is on its own circuit, there should not be Power Factor/ harmonic distortion issue. I'm blaming bad Sushi. Advise? Thanks db
    The Off-grid inverter has a generator power input? If so have you tried starting the heat pumps while the backup generator is assisting the inverter.
    8 kw inverter should have a peak power of at leat 16 kw momentarily. This should be sufficient.
    Power factor may be at fault. Some inverters can be programmed for powerfactor corection. Inductive loads will cause the powerfactor to be less than one.
    Capacitor banks could help.
    Good luck

    Sent from my SM-G900W8 using Tapatalk

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365