Results 1 to 13 of 14
-
02-25-2013, 12:40 PM #1
need a condensing unit for a weber coffin type freezer.(weber)
weber is out of business and the condensing unit is wrong and really old heres some numbers:
unit: weber coffin type freezer # C-TV-12IC/ Ser#1R102816
compressor is a 90-1.50 a medium temp compressor
the condensing unit really needs to be trashed..freezer is 60' away from condenser and line sets are under ground.
like all my customers this guys broke.
-
02-25-2013, 01:00 PM #2
I couldn't even find a mention of Weber, so no info seems likely.
Based on single deck frozen food or ice cream case from 30 years ago, they generally required 450-500 Btuh/ft so between 5400-6000 Btuh at -25ºF SST for frozen foods (or -35ºF SST for ice cream) should work OK for a 12 footer.
-
02-25-2013, 01:09 PM #3
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
-
02-25-2013, 01:10 PM #4
this icemeister ill look for one..
-
02-25-2013, 01:11 PM #5
yes powell it is a semi compressor, this place is a mess, and was put together with junk
he knows i won't continue the practice..and will replace the condensing unit with what is correct..
-
02-25-2013, 02:01 PM #6
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
The 90-150 (EAB-0150) is a MT12/LT502 compressor as I stated but the LT502 use is an alternative application for which I cannot find any btuh specs.
Based on it's CFH and the S.W.A.G theory I would guess it's LT502 btuh's are very close to what Icemeister listed.
-
02-27-2013, 12:34 AM #7
got a quote today for $2755,,,,MY CUSTOMER IS GOING TO COUGH UP HIS LIVER..
-
02-27-2013, 08:43 AM #8
I've had very good experience with the newer hermetic low temp units...and they save a boatload of money.
Look at a Copeland FJAL-B301-TFC.
-
03-01-2013, 07:50 PM #9
wii do, thanks.
-
03-10-2013, 07:38 PM #10
-
03-10-2013, 08:48 PM #11
Here's a link to the Copeland info (See p.9): http://www.hvacrinfo.com/CopelandUni...DS-4_MandF.pdf
-
03-10-2013, 09:07 PM #12
wow a 3 hp system.....Ok, thanks..
-
03-11-2013, 10:38 AM #13
A 3 HP unit does appear to be big for this application...if you're comparing it to what the semihermetics will do...but going by the estimated loads I stated of 5400-6000 Btuh at -25ºF SST for frozen food (or -35ºF for ice cream) the FJAL-B301 would be the one to go with.
While the FJAL-A225, at a rated 5380 Btuh at -25ºF SST is a tad shy of what we need for FF, it's close enough that it might work OK...but I'd feel a lot better with a little extra, especially when you consider that we're taking a wild guess at what the load really is for that old case.


Reply With Quote