Thread: rheem over temp limit error

  1. #1
    Join Date
    Feb 2013
    Posts
    7
    Post Likes

    rheem over temp limit error

    I have a rheem 90 plus series model number rgfd07emcks over temp limit error 33, right when the unit starts up cold it flashes code 33 over temp limit. I have used the volt meter took it all the way to the board. I could not find an open anywhere. I then jumpered the whole circuit at the board still got the same code. I figured it was a bad logic board so I changed out the board however still have the same error code. '
    Does anyone have any ideas

  2. #2
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    233
    Post Likes
    Are you the service tech, or the homeowner??????

  3. #3
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Could be a lot of things. Is is a two pipe setup?


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  4. #4
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Hmmm... RGFD... that is a MOD furnace (modulating). You really need to get a RHEEM guy out there... this furnace is unique... not an average unit and not easy to service unless one understands the unit.

    Furnaces are not DIY products... folks can cause a lot of damage and potentially create an unsafe condition if they try.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  5. #5
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by stuff350 View Post
    I have a rheem 90 plus series model number rgfd07emcks over temp limit error 33, right when the unit starts up cold it flashes code 33 over temp limit. I have used the volt meter took it all the way to the board. I could not find an open anywhere. I then jumpered the whole circuit at the board still got the same code. I figured it was a bad logic board so I changed out the board however still have the same error code. '
    Does anyone have any ideas
    Jumping things out on that board can screw the board up.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  6. #6
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    233
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Hmmm... RGFD... that is a MOD furnace (modulating). You really need to get a RHEEM guy out there... this furnace is unique... not an average unit and not easy to service unless one understands the unit.

    Furnaces are not DIY products... folks can cause a lot of damage and potentially create an unsafe condition if they try.
    Thats what I was getting at, just from the post theres a possible drowning situation there.

  7. #7
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by TriWorksInc View Post
    Thats what I was getting at, just from the post theres a possible drowning situation there.
    Yeah... If this guy is trying to DIY this furnace problem... he may spend a LOT more $$$ on his learning curve than calling a Rheem person and paying them to do the work properly... not to mention all the time, aggravation, and possibly nights on the couch 'cause mama is cold and irritated...
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  8. #8
    Join Date
    Feb 2013
    Posts
    7
    Post Likes
    Thread Starter
    Sorry, I was not specific when I said jumped it at the board, I'm an OSU -it student in the HVAC program and am working on this project for extra credit. I jumped it from the back side of the plug before it goes into the board .

  9. #9
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    233
    Post Likes
    What I do is work with the tech manual right in front if me? There are too many mistakes that can be made with electrical troubleshooting and you need to follow protocol while troubleshooting and don't use jumpers in the wrong places, good luck.

  10. #10
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Check for three things:
    Faulty limit control
    Insufficient combustion air
    Unstable flame pattern


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  11. #11
    Join Date
    Feb 2013
    Posts
    7
    Post Likes
    Thread Starter
    The burner don't fire off at all right away it gives off that high limit error

  12. #12
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Might clear the board... then start over... sometimes codes get 'stuck' in a board... power off and count to 10... then power back on.

    If you are in school and doing a project... I would go through the entire troubleshooting chart in the IOM manual (I assume they gave you the manual)... sooner or later you will find something of interest.

    Then when you KNOW what was related and what was not... you can explain the WHY's of what was wrong and how to fix it.

    Knowing the WHY's is the key to this industry... otherwise... one becomes a parts changing hack.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  13. #13
    Join Date
    Feb 2013
    Posts
    7
    Post Likes
    Thread Starter
    I like that point you made with the parts changing hack, there isn't much of a manual that came with the unit and yes I did clear the board even changed the board.

  14. #14
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    The WHY's are the key to being successful (technically) in this business.

    I suspect if you approached the faculty at your school... they could find you a current IOM (installation and operations manual) manual for that furnace. Give them the model and serial... and see if they can get it for you.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  15. #15
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    It's cold. It flashes an open limit before it fires. You've replaced the board and still get an open limt error before ignition. And you could not find any open safeties?

    How exactly did you confirm the limit was closed?

  16. #16
    Join Date
    Feb 2013
    Posts
    7
    Post Likes
    Thread Starter
    I checked with a volt meter

  17. #17
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Quote Originally Posted by stuff350 View Post
    I checked with a volt meter
    Seems to me you've caught the extremely rare impossibility.

    Please let us know the resolution. And be very cautious when jumping around safeties. Especially if anyone you care for is living upstairs.

  18. #18
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by stuff350 View Post
    I like that point you made with the parts changing hack, there isn't much of a manual that came with the unit and yes I did clear the board even changed the board.
    It's a school project and they don't have a manual?

  19. #19
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by Joehvac25 View Post
    It's a school project and they don't have a manual?
    Sounds like a couple of other schools I attended decades back...
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  20. #20
    Join Date
    Feb 2013
    Posts
    7
    Post Likes
    Thread Starter
    Waiting iom manual, to come in ill let you guys know what's wrong with it when I find out. Just also found out students have been trying to trouble shoot this unit for a year now to try to figure out what's wrong with it

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •