new problem, i have a retail customer with several 5 door ice cream cases. they are using a small rack system {protocol} with eprs on the frozen bunkers only. One of the 4 ice cream cases has a ball of ice that keeps building up arround the txv. It takes about 10 days to start becoming noticable and i have defrosted it for the third time. the doors all shut ok, the gaskets are new, and i haven't found any other access for air to leak in. this case is allong side of another just like it that does not have any build up. they are back to back with two medium temp cases and the other two ice cream cases are across the isle. The defrost is set for 4 per day and 22 min. long each. they are electric defrost and staggered with the other cases so that only one is in defrost at a time. the heaters all work and i have disconnected the early termination stat for this case but that did not seam to have any effect. An "educated engineer" from H P suggested " put a heat tape there". Anybody with a better idea?
-
01-28-2013, 08:38 PM #2
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 905
Check and adjust sh to 4-6 degrees area... But first I would pump that circuit down and clean the txv screen.
Does the ice cause the case to run warm??
-
01-28-2013, 09:21 PM #3
Ok, kind of hard to decipher what you're talking about.
You've got a 5 door ice cream case that the TEV is turning into a ball of ice.
It's electric defrost 4x daily for 22 minutes?
#1. Set the TEV and do as Dchappa suggested.
#2. Why do you need 4 electric defrosts? That's an unusual setup, in my experience. Door cases typically only need one defrost daily and an electric defrost typically wants to be longer than that.
-
01-28-2013, 11:06 PM #4
-
01-29-2013, 12:11 AM #5
Regular Guest
- Join Date
- Jan 2013
- Location
- Northern CA
- Posts
- 25
Sounds like the HP engineer must have worked at Source or one of those other slacker companies...
-
01-29-2013, 12:51 AM #6
Interpret: (4) five door low temp cases with epr valves. Not sure: the med temp are/are not on the same system. Question: refrigerant type, sight glass status, is this rack on heat reclaim, and as stated above (SH on all four cases).
Has it had this problem before? yes-what has been done (even if it didn't work), no-what changed.
If these have DTS's then lengthen the time as JP pointed out, let the temp terminate.
TXV screen blockage is a strong possibilty (Dchappa), as is an insufficient charge.
HP=HewlettPackard? hahaha
-
01-29-2013, 12:52 AM #7
Interpret: (4) five door low temp cases with epr valves. Not sure: the med temp are/are not on the same system. Question: refrigerant type, sight glass status, is this rack on heat reclaim, and as stated above (SH on all four cases).
Has it had this problem before? yes-what has been done (even if it didn't work), no-what changed.
If these have DTS's then lengthen the time as JP pointed out, let the temp terminate.
TXV screen blockage is a strong possibilty (Dchappa), as is an insufficient charge.
HP=HewlettPackard?
why the double post?
-
01-29-2013, 01:11 AM #8
Wanna see she this goes.
Sent from my SGH-T999 using Tapatalk 2
-
01-29-2013, 07:26 AM #9


Reply With Quote
BUAHAHAHA that's awesome!