Results 1 to 11 of 11
  1. #1
    Join Date
    Jan 2013
    Posts
    5
    Post Likes

    Confused White-Rogers Thermostat - Heat Won't Shut Off

    Hello,

    I just moved into a new house last week and I'm having an issue with the upstairs thermostat. I'm a first time home owner and looking for some guidance on how to troubleshoot the problem. An explanation of the issue is below.

    We have two heat pumps and two thermostats - one for downstairs and one for upstairs. The downstairs unit works great but the issue is with the upstairs thermostat.

    The heat was working fine for the first two days, but when I came home from work on Friday I went upstairs and noticed it was stifling hot. The thermostat was set at 60 but the room temperature was 90 and was continuously blowing out of the vents upstairs. So the heat must have been blowing all day and it never shut off when it reached the desired temperature. The settings on the thermostat were at Auto Fan and Heat, which are the correct settings to my knowledge.

    To get around the problem, I just turned off the upstairs unit and it did shut off for me. However, the same thing happened the next day when I turned it on again - the heat kept running after reaching the desired temp...in excess of 15 degrees. This time, however, the heat would not shut off when switched to the "off" position. I left it go for about an hour and tried it again and it then finally did shut off.

    I am now afraid to turn it back on because I'm worried I will not be able to shut it off.

    Here are the specs on the thermostat

    white-rogers comfort-set standard 1F89-211 pro-spec #80h∅w

    Any advice that can point me in the right direction would be a huge help. Thank you!

    - Nick

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,704
    Post Likes
    now would be the appropriate time to call/find a competent service company.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,044
    Post Likes
    its most likely not the thermostat. also now would be a good time to find the circuit breaker for the airhandler
    Go Trump

  4. #4
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Thank you! I appreciate the advice.

  5. #5
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    Post Likes
    My best guess would be that its a stuck on relay for the emergency, or axillary heat. Thermostats are usually not the problem, but it could be. Was the outdoor unit running when you experienced the stuck on heat problem?
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  6. #6
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by Kevin Weaver View Post
    My best guess would be that its a stuck on relay for the emergency, or axillary heat. Thermostats are usually not the problem, but it could be. Was the outdoor unit running when you experienced the stuck on heat problem?
    That's a good question, but I can't give you a definite answer. I want to say it was, but I didn't go outside to check at the time so I can't say for sure. I checked the outdoor unit after the heat went off to see if there was anything that stood out. The only thing I noticed was that there was ice around the cords that go from the unit to the house - not sure if that can have an effect though or not?

    If I want to turn on the heat again upstairs to test out the system and it doesn't shut off, is it okay to use the breaker as a last resort? I wasn't sure if that would damage the system by suddenly shutting off the power to it.

  7. #7
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    Post Likes
    Now it sounds like there is a low voltage short because you say there was ice on the pipes. That means it was in the a/c mode of operation. It could be the thermostat, now that you say that there was ice on the pipes. It could be a low voltage short. Sounds like you need a professional to diagnose system.

    And yes, it is okay to shut those breakers off.
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  8. #8
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by Kevin Weaver View Post
    Now it sounds like there is a low voltage short because you say there was ice on the pipes. That means it was in the a/c mode of operation. It could be the thermostat, now that you say that there was ice on the pipes. It could be a low voltage short. Sounds like you need a professional to diagnose system.

    And yes, it is okay to shut those breakers off.
    Well I should clarify that it did just snow here (Eastern PA) so the ice was probably from the weather. I just didn't know if having ice on those pipes would disrupt how the unit operates.

    Regardless, sounds like I should have someone come look at it since the issue is uncertain. Thank you for your input, much appreciated!

  9. #9
    Join Date
    Jul 2011
    Location
    indiana
    Posts
    58
    Post Likes
    You can swich first floor tstat with second and see if does same thing. NO it does not mean it was in AC if there is ice on pipes.......

    Sent from my SGH-T999 using Tapatalk 2

  10. #10
    Join Date
    Jan 2013
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by newinthefield View Post
    You can swich first floor tstat with second and see if does same thing. NO it does not mean it was in AC if there is ice on pipes.......

    Sent from my SGH-T999 using Tapatalk 2
    Very good idea, didn't think of that. Thank you!

  11. #11
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,704
    Post Likes
    don't let the magic smoke out if you go to swapping t-stats.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.