Results 1 to 7 of 7
  1. #1
    Join Date
    Feb 2003
    Location
    garland, texas
    Posts
    701
    Post Likes

    suction line trap

    Hope this is correct forum. We're installing a split wine unit for wine room. The refrigerant piping instructions call for a trap in suction line half way up between condenser and evaporator. The evaporator is 20' above condenser. What is the purpose of this trap? I've seen traps in suction line when condenser is above evaporator.

  2. #2
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    4,846
    Post Likes
    Were is the compressor in relation to the evaporator?

  3. #3
    Join Date
    Dec 2011
    Location
    Northeast PA
    Posts
    222
    Post Likes
    If I recall correctly it is for proper oil return. With out the traps they oil settles in the wrong locations and will cause damage.

  4. #4
    Join Date
    Feb 2003
    Location
    garland, texas
    Posts
    701
    Post Likes
    Thread Starter
    condenser/compressor is 20' below evap and 45' total refrigerant line length.

  5. #5
    Join Date
    Dec 2011
    Location
    Northeast PA
    Posts
    222
    Post Likes
    Name:  piping.JPG
Views: 8336
Size:  66.1 KB

  6. #6
    Join Date
    Sep 2012
    Location
    USA
    Posts
    1,085
    Post Likes
    Quote Originally Posted by nvr2old View Post
    condenser/compressor is 20' below evap and 45' total refrigerant line length.

    Just thought I would point this out as it seems to have been missed.

  7. #7
    Join Date
    Dec 2011
    Location
    Northeast PA
    Posts
    222
    Post Likes
    you are right i did miss that... these long days are killing me.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.