Results 1 to 7 of 7
Thread: suction line trap
-
01-28-2013, 11:55 AM #1
Professional Member
- Join Date
- Feb 2003
- Location
- garland, texas
- Posts
- 540
suction line trap
Hope this is correct forum. We're installing a split wine unit for wine room. The refrigerant piping instructions call for a trap in suction line half way up between condenser and evaporator. The evaporator is 20' above condenser. What is the purpose of this trap? I've seen traps in suction line when condenser is above evaporator.
-
01-28-2013, 04:30 PM #2
Were is the compressor in relation to the evaporator?
-
01-28-2013, 05:58 PM #3
Professional Member
- Join Date
- Dec 2011
- Location
- Northeast PA
- Posts
- 202
If I recall correctly it is for proper oil return. With out the traps they oil settles in the wrong locations and will cause damage.
-
01-28-2013, 06:18 PM #4
Professional Member
- Join Date
- Feb 2003
- Location
- garland, texas
- Posts
- 540
condenser/compressor is 20' below evap and 45' total refrigerant line length.
-
01-28-2013, 06:27 PM #5
Professional Member
- Join Date
- Dec 2011
- Location
- Northeast PA
- Posts
- 202
-
01-28-2013, 06:48 PM #6
Professional Member
- Join Date
- Sep 2012
- Location
- Central Florida
- Posts
- 687
-
01-28-2013, 06:52 PM #7
Professional Member
- Join Date
- Dec 2011
- Location
- Northeast PA
- Posts
- 202
you are right i did miss that... these long days are killing me.


Reply With Quote
