01-28-2013, 08:26 AM #1
New Guest
- Join Date
- Aug 2008
- Location
- Upstate NY
- Posts
- 4
Freezestat for 20" ductwork
Hello,
I was hoping someone had a suggestion for a freezestat with a very short cappilary.
I know ACI has one with a 6', but I was hoping for something smaller, as the ductwork I need to put it in is only 20".
I think I remember working with one that had a 3' capilary years ago for some unit venitalators, but I don't remember the manufacturer.
Thanks for any help.
-
01-28-2013, 12:36 PM #2
New Guest
- Join Date
- Jan 2013
- Posts
- 1
In the past we've used larger capillary tubes on smaller ducts by mounting them attached to a section of conduit. Cut a hole (smaller than 4"x4") on both sides of the duct, take 2 4x4 box covers (drill a hole for a box connector) and attach a box connector right in the middle of each, put a piece of conduit between the 2 and attach the capillary around it, feed it out a slot in the conduit thru the opposite side of the duct and mount the 4x4 box covers on each side of the duct with a bit of caulk.
The box connectors end up going on the inside of the duct to support the conduit between each side. You don't have to worry about the set screw since it will be wedged between both sides of the duct once the other side is attached. Feed the capillary out a slot in the edge of a box cover and mount the device on the outside of the duct.
Makes perfect sense to me, but I've seen it a bunch. Hopefully I've described it sufficiently.
-
01-28-2013, 02:45 PM #3
Professional Member
- Join Date
- Nov 2006
- Location
- Desert Southwest
- Posts
- 400
Good first post. I have also seen this done quite a bit .
If you can't fix it with JB Weld, Duct Tape, and Ty Wire it has to be replaced.
No good deed goes unpunished.
If you want to take off friday to go fishing then make sure you train your helper right.
-
01-29-2013, 08:14 AM #4
Professional Member
- Join Date
- Jul 2008
- Location
- Seattle, WA
- Posts
- 49
I haven't seen one but as another alternative we usually just roll the 7' freezestat up in a nice neat circle in those cases. Works well and I doubt a smaller freezestat will save you much cost if any. Good luck.
-
01-29-2013, 08:30 AM #5
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,709
There are shorter capilary line stats , called FROST STATS for use on heat pumps adjustable 14 to 54 F range
-
01-29-2013, 03:58 PM #6
New Guest
- Join Date
- Aug 2008
- Location
- Upstate NY
- Posts
- 4
Thanks for the responses. I'm going to go with Autonerds suggestion, seems that will do the trick.
-
01-30-2013, 07:45 AM #7
Regular Guest
- Join Date
- Aug 2011
- Location
- Denver PA
- Posts
- 24
If the area outside of the duct is heated you do not have to place all of the element in the duct. I have also used the conduit method to mount low limits in small ducts