    I have had to repair several units recently that had bad schraeders including one less than a year old. The cheap plastic caps with missing gaskets did not help.

    Rub through leaks are usually tough because they often do not hiss or bubble the soap until you get the two pieces spread apart a bit.

    Sent from my SGH-I747M using Tapatalk 2

  2. #15
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,351
    Quote Originally Posted by cswenson218 View Post
    Thanks for the advice, everyone...I like what Helioson said: you know it's leaking somewhere...don't leave til you find it. I think a lot of it is just "Don't give up."
    Just ask yourself, what would fengshvac do? I carry a very small spray bottle with bubbles in it a spray all valve stems down before hooking my gauges and after removing my gauges EVERY TIME, once you do it a few times its just a habitual part of the process. And yes it has a lot do do with not giving up, I can do anything some things just may take me a little longer than the next guy.

  3. #16
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,509
    Quote Originally Posted by jtrammel View Post
    Just ask yourself, what would fengshvac do? I carry a very small spray bottle with bubbles in it a spray all valve stems down before hooking my gauges and after removing my gauges EVERY TIME, once you do it a few times its just a habitual part of the process. And yes it has a lot do do with not giving up, I can do anything some things just may take me a little longer than the next guy.

    Betcha feng just needs to look at a leak and it will repair itself.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #17
    Join Date
    Nov 2007
    Location
    Tucson, AZ
    Posts
    94
    Had one system that was low saw oil but condenser fan sprayed it all over hit it with nitrogen could not find it no pressure drop keep looking finally decided to remove on guage at a time and as soon as I moved the tubing it started hissing. it was factory discharge off compressor at a 90 bend... move things and wiggle it see if it wont make some noise or drop pressure

  5. #18
    Join Date
    Jan 2013
    Location
    Northern CA
    Posts
    25
    Buy a good leak detector, IV used a TIF ZX for 10 years and once you learn how to use it, it will be the best leak detector. Always carry a halide leak detector and soap bubbles. Take your time and you will find it, most leaks are missed because you over rush it.

  6. #19
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    521
    Quote Originally Posted by N2fords View Post
    Had one system that was low saw oil but condenser fan sprayed it all over hit it with nitrogen could not find it no pressure drop keep looking finally decided to remove on guage at a time and as soon as I moved the tubing it started hissing. it was factory discharge off compressor at a 90 bend... move things and wiggle it see if it wont make some noise or drop pressure
    To the OP,
    Of course you'll be wearing your safety glasses; I had a co-worker grab a line only to have it snap off and a stream of liquid refrigerant shot by his ear. He started wearing them after that...

    With water cooled units, the condensers like to corrode and leak refrigerant into the waterside of the coaxial tubing. Shut the water off, put a rubber glove over the end and see if it inflates before tripping on high head pressure cutout. Have your leak detector ready to sniff the inside of the glove when you remove it.

    If you confirm a leak in the w/c condenser keep the refrigerant pressure up until the replacement can be made or you run the risk of contaminating the whole system with moisture.

    Keep in mind refrigerant is heavier than air, start high and work low. Make yourself a checklist of where you find leaks in the order of easiest to hardest. Start with your eyes and ears first. Look for oil or wind effect and listen for hissing, whistling or sputtering of refrigerant through oil. Don't be afraid to shut off noisy equipment if you are confident you can restart it.
    Read the threads on this site regularly and you will pick up a serious amount of knowledge as well as discover who the pros are over time.
    :beer:

  7. #20
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Definitely ask where the other guys found the leaks you could not and how they found them, that's how we learn. If its there you can find it. Do not eat hours on a leak test!!! You didn't make the leak. Most will be in obvious locations or oil will lead you to them. Most not all. If its a pump down system use a solenoid magnet and open the LLS valve and equalize the pressure, if its on low side and you leave it pumped down may be very hard to find. I got bit once by a leak on the mounting stud on an accumulator, on the bottom, leaking. Took all day to find it but now I check for that and have found probably 4 or 5 over the years. Rusted accumulators will leak through the pits so check the whole thing not just the connections. Patience and persistence grasshopper. It's a process. You'll get it.

  8. #21
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    521
    Quote Originally Posted by Tommy knocker View Post

    Do not eat hours on a leak test!!!
    You didn't make the leak.

    I got bit once by a leak on the mounting stud on an accumulator, on the bottom, leaking.

    Rusted accumulators will leak through the pits so check the whole thing not just the connections.
    1) Great advice!

    2) Yup

    3) That means factory welds too.

  9. #22
    Join Date
    Dec 2012
    Location
    Spokane, Washington
    Posts
    121
    Quote Originally Posted by Tommy knocker View Post
    Do not eat hours on a leak test!!! You didn't make the leak.
    I'm not suggesting eating hours on every job, or if you "get it" then not at all.

    If an inexperieced, impatient, new tech isn't finding leaks and continues to have more experienced tech's coming behind him finding leaks....well....he's gonna be looking for a new career soon.

    To this day, if I make a mistake that I know I could've avoided, I "eat" the time. You don't have to and I don't HAVE to, but that's what I was taught and that's what I'll do.

    If a new tech can find a company and/or customer to pay him to sit there trying to figure it on their dime, then that's great. Charge them until they squeal.

    My point is that most new guys (I was the same way), think they can just do their "eight" and all is well. OK, whatever.

    I apologize to anyone who took this the wrong way. You absolutely do not HAVE to eat any hours, ever.

    OP: If you want to excell in ANY career you are going to have to put some TIME in to stand above the crowd. Have you ever heard of an athlete putting in some extra hours on the field, or a office guy staying late to wrap up a project, or how many techs get paid for extra training (some do, I know, but some don't). Best of luck to you and I hope you figure it out soon.

  10. #23
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by Helioson View Post
    I'm not suggesting eating hours on every job, or if you "get it" then not at all.

    If an inexperieced, impatient, new tech isn't finding leaks and continues to have more experienced tech's coming behind him finding leaks....well....he's gonna be looking for a new career soon.

    To this day, if I make a mistake that I know I could've avoided, I "eat" the time. You don't have to and I don't HAVE to, but that's what I was taught and that's what I'll do.

    If a new tech can find a company and/or customer to pay him to sit there trying to figure it on their dime, then that's great. Charge them until they squeal.

    My point is that most new guys (I was the same way), think they can just do their "eight" and all is well. OK, whatever.

    I apologize to anyone who took this the wrong way. You absolutely do not HAVE to eat any hours, ever.

    OP: If you want to excell in ANY career you are going to have to put some TIME in to stand above the crowd. Have you ever heard of an athlete putting in some extra hours on the field, or a office guy staying late to wrap up a project, or how many techs get paid for extra training (some do, I know, but some don't). Best of luck to you and I hope you figure it out soon.
    Good and valid points. If I bone head something then I'll fix it on me to a point. Looking for a leak is not a bone head on me though. Some leaks are easy some are not. Every new tech and experienced are constantly learning and yes the customer or shop should pay us for that. IMHO.

  11. #24
    Join Date
    Dec 2012
    Location
    Spokane, Washington
    Posts
    121
    Ok..I'm reasonable "to a point" Let's use YOUR words...
    bonehead, defenition /'bon,hed/ noun: stupid person
    1. these words used to express a low opinion of someone's intelligence.
    2. being a college course for students lacking fundamental skills.
    3. as used in HVAC/R: to charge a system that one believes has a leak, then ineptly perform a leak check with no results, and then walk away from said system.
    Bonehead IMHO

  12. #25
    Join Date
    Dec 2012
    Location
    Spokane, Washington
    Posts
    121
    Tommy knocker, OP and all other members...please forgive me for being so passionate about my opinion. We all know what they say about opinions. In rereading my posts I realize that they may seem argumentative and borderline defamatory. I in no way want to portray this attitude. I fully respect all people who would attempt to make a career of this business. OP-keep at it, you'll get it. Tommy knocker-if you ever find yourself in the Pacific Northwest...e-mail me and I'll buy you a dinner and a drink. Thanks for your understanding,
    Helioson

  13. #26
    Join Date
    Mar 2010
    Location
    Houston
    Posts
    98
    1. There are different types of detectors. Understand them and make sure yours is/are good ones! I like my Fieldpiece.

    2. Keep sensor clean!

    3. Switch detector on in clean air - as most units calibrate at power up. (This bites a lot of guys).

    4. Go SLOW and steady when sweeping sensor tip, and keep it dry.
    5. Refrigerant being heavy will show best underneath fittings and valves. It will collect low in case and housings sometimes making it worth a poke w detector.
    6. Newer installs usually start with connection points and welds. Older r22 units 15+ years ill jump right to evap.
    Small condenser coil leaks can be a real bugger outside. Especially on breezy days. A non-permeable cover can help (system off).
    7. Operating pressure via nitro is very helpful. Sometimes you'll hear it with unit off but at op pressure.
    8. Oil is key indicator.
    9. Blue bubbles are amazing at exposing schrader valve and flare leaks.
    10. It's a sealed system. There should be NO leakage. You can find it. Did I mention SLOW & steady?

    K

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event