Results 1 to 6 of 6
  1. #1
    Join Date
    Feb 2008
    Location
    Belize
    Posts
    24

    sporlan oil level control

    sporlan valve OL-60XL; I got oil flowing up to inlet screen of control but not oil is filling crankcase. I check inlet screen but it not plug up . oil pressure in supply line to control is 40 psi. crankcase pressure is less than that so i believe this oil level control might be clog.
    is this control serviceable or do i have to replace it?

  2. #2
    Join Date
    Jun 2009
    Location
    Garland, TX
    Posts
    362
    http://sporlanonline.com/110-10_012008.pdf

    Page 6 on this Sporlan bulletin tells how to adjust the control. *Note: I only found this by searching, because I was very curious; I have never actually adjusted one. Good luck.
    Last edited by trippintl0; 01-27-2013 at 06:48 PM. Reason: forgot link

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    21,308
    They aren't field serviceable.

    If you've determined that it's bad, replace it.

    Don't forget the o-rings.

  4. #4
    Join Date
    Feb 2008
    Location
    Belize
    Posts
    24
    Thanks for confirming that. I will replace it.Have a great day , to day ! special thanks to tripointIO and jpsmith1cm

  5. #5
    Join Date
    Jan 2013
    Location
    Northern CA
    Posts
    25
    IV replaced plenty of them, make sure to never go 10 turns from the top or the ball could fall off...

  6. #6
    Join Date
    Feb 2008
    Location
    Belize
    Posts
    24
    Thanks for the Info. I found a Baker Dis.shop in Doral FL., A manager by the name of Tony Peres. He had one so I arranged to have him fedex the oil level control to us, this is for the 10 hp compressor Copeland. Thanks Tony!! This forum makes me happy because I can talk to other people who are doing the same thing and there always somebody there. This is my face book. Thanks all the people at HVAC TALK.