Heat pump not working? Help please
Hello. First, some background info. This is my first winter in a home with an electric heat pump so I'm very new to this. I live in MD and it has been as cold at 10 degrees recently. My heat pump has been blowing what feels like cold air for days. After doing research, I am beginning to understand that this is normal and that it's not truly 'cold' air. I usually keep my thermostat set to 67 degrees. I have noticed that when I turn it up to 70 or more that I get warm air out of the vents and my house actually heats up. If I leave it at 67 all the time it seems that my heat pump is running constantly and my thermostat says that it's 65 to 66 and it never seems to warm up. Is there something wrong?
-
01-27-2013, 09:56 AM #2
New Guest
- Join Date
- Jan 2013
- Posts
- 3
I also want to add that I don't have an emergency option on my thermostat.
-
01-27-2013, 12:11 PM #3
post a photo or model number of the thermostat, no emerg is rare.
at those temps the heat pump will run constantly, but should be able to maintain temp once it is reached.
the warm air you feel means the aux/emerg is running- you have gas, electric, propane or oil for that.If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
01-27-2013, 12:21 PM #4
Post pic of your thermostat, sounds like an older stat. they often did what you describe.
-
01-27-2013, 12:50 PM #5
New Guest
- Join Date
- Jan 2013
- Posts
- 3
We have a Radio Thermostat C30. It does have an emergency setting, it just wasn't obvious at first. I have also read that the emergency setting is for true emergencies, such as your heat pump was crushed by a falling tree or a meteor, Volkswagen, etc.
It struggles to get to 67, which is what we have set. It heats to about 65 or 66 degrees but the air is cool to the touch. The aux heat is an electric coil but that doesn't seem to kick in unless we set the target temperature to be well above the current temperature (72 or more).
This is our first heat pump. Being from NY, we're used to gas or electric furnaces.
Thanks!
-
01-27-2013, 12:54 PM #6
Sounds like your heat pump needs service, with tightly sealed and insulated ducts you will get ~100-110F air out of vents and ~110-120*F out with electric aux and heat pump running.
-
01-27-2013, 03:35 PM #7
-
01-27-2013, 07:49 PM #8
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
sounds like it is not cycling the auxillary heat ,
The governent can not give anything to someone that it has not first taken from someone else
-
01-27-2013, 08:09 PM #9
From your description, I think your system is working properly. Here's why.
The thermostat has two mercury bulbs. One is "first stage" which is the heat pump. The second mercury bulb is "auxiliary heat", the heating elements. As it gets colder outside the efficiency (and output temperature) of the heat pump goes down. When the heat pump cannot satisfy the thermostat the temperature in the house drops a little more and then the thermostat activates second stage heat. That raises the temperature only enough to satisfy the second stage mercury bulb but not enough to satisfy first stage. The heat pump continues running but the output temperature may be lower than body temperature so you perceive the air as "cold." This is way older thermostats work.
Before we installed a digital thermostat our house would stay at 70* until the outdoor temperature fell below 30*. Then the house would stay at 68* (2* was the difference between the first and second stage bulbs.) We would compensate by raising the setting of the thermostat to 72* so the house stayed at 70*. When the temperature outside rose above 30* the heat pump could raise the house temperature so we then had to return the thermostat to 70*.
Digital thermostats have much closer tolerances so they do not let the temperature drop so far before activating second stage.
If you want to call a service company to check you system go right ahead but I suspect they will find it as I described.
-
01-27-2013, 08:13 PM #10
BTW, I'm not familiar with the Radio C30 thermostat. Is that Radio Shack?
Mercury thermostats are not as precise as digital ones but they work adequately once you know what to expect.
-
01-28-2013, 12:11 AM #11
http://www.radiothermostat.com/docum...on-19apr10.pdf
maybe it is one of these.If Guns Kill People, Do Pencils Misspell Words?