    Compare Heat Pumps - Broan FT4BI iQ Drive vs.Trane XL20i
    Any comments? Which is more efficient, reliable, comfortable, less prone to malfunction or mfg. defects?
    Reference my other threads regarding Manual J and sizing a replacement heat pump for my 1827sf Florida home with too many windows. LOL
    jtrammel sent me to the Comfort Institute website and the Maytag/Broan dealer actually came out and did a whole house evaluation, including blower door test, flow hood evaluation, house and window measurements, insulation R-value, and load calc. He didn't ask or care about the size of my old system, and said it didn't matter because the load calc (which he did on his computer after he got the test results and took measurements) would determine the correct size for the replacement. He's working up a quote on two equipment options that he'll email me in a few days. He did leave the infiltration and duct leakage reports with me, but of course, he didn't leave me with a copy of the Manual J results (I guess so it can't be used by someone else). However, he discussed his Manual J results with me and compared them with the Manual J printout I received from the Lennox dealer. Both load calc's were very close and both recommended a single stage system capable of 42000 BTU.
    When we got into the discussion of dual stage and/or multi-stage options, he explained very clearly the differences in cooling performance between dual stage and/or dual compressor units and the IQ Drive multi-stage compressor. At design conditions, both dual stage and dual compressor units max out at the rated tonnage, i.e., the most cooling you'll get from a 3 ton is 36000 BTU. With the multi-stage operation of the IQ Drive compressor, it maxes out at 118% of rated tonnage. That is, a 3 ton IQ Drive will provide up to 42480 BTU (3.5 ton)
    Based on Manual J load calculation he recommends either the 3 ton 21 SEER Broan FT4BI iQ Drive, or the 4 ton 16 SEER Broan FT4BF.
    The best part is that Broan is an RE Michel brand and this dealer can get the equipment through RE Michel for me practically wholesale using my son's employee discount (he manages the Orlando RE Michel). I'm hoping this brings the overall cost into my price range, but we'll see.
    What do you all think?
    Delaware
    http://www.ahridirectory.org/ahridir...ultSearch.aspx
    I would really check that claim out.......
    Always here
    Broan is a nordyne product , the install of the iq drive unit is very important to acheive operation .it does sound like they are addressing your sizing concerns properly .make sure you get a 10 year part and labor warranty on the unit and go with it
    The 3 ton Broan rates at 21.00 SEER, 13 EER and 9.60 HSPF. Cooling capacity is 35,000 so I don't know why a 3 ton would work for the IQ drive but you need a 4 ton for the BF which is rated at 36,000 BTU.
    The XL20i 3 ton with TAM8 is 18.50 SEER, 13 EER and 9.50 HSPF.
    Hard to beat a system with son's discount though. The Broan Quality Pledge replaces the whole outdoor unit if you lose the comp in 10 years (registered.) We have a guy with an A-S 2 compressor heat pump that lost its small compressor twice now. A-S says takes 3 failures to get help besides a new compressor.
    Florida Space Coast
    Didn't you mean 48,000 BTU for the 4 ton? If I went with the Trane XL20i, it would have to be the 4 ton, SEER 17.75.
    The 10 year Quality Pledge does sound good.
    Florida Space Coast
    Quote Originally Posted by energy star View Post
    I'm pretty sure the AHRi site reflects nominal BTU ratings only, not actual equipment performance data for various ODDB/IDWB and t-stat setpoints. I believe the latter data is proprietary and not readily accessible by laymen on the Broan website.
    I could be wrong.... it's happened before. LOL
    Portland OR
    They rate them at 100% of capacity for AHRI numbers so they can get higher efficienies but they actually have a capacity that as stated is 118% of rated so it does give a 3.5 ton cooling capacity on a 3 ton unit. The efficiency drops below the 21 SEER rated at any point above 100% so it would work in this homeowners case.
    I have installed the Frigidair iQ drive heat pump with their modulating gas furnace and the quality of it is NOWHERE near Trane but its a great product overall. Its been on the market longer than the other variable drive options and we installed the frigidaire system 2 or 3 years ago and have not had a problem at all with it.
    Florida Space Coast
    Quote Originally Posted by SkyHeating View Post
    Thanks! Since I joined this forum, I've really appreciated your input... not only on my issues, but your comments throughout the AOP Residential group. And I think I've seen all your youtube videos on the Trane systems.
    Can you tell me some of the important differences you've observed between the Hyperion a/h and the one supplied with the Broan equipment? I don't have the specs or p/n of the Broan, but I'm told they're not near as tall as the Hyperion, so I could accomodate a media filter with the Broan without modifying my a/h stand. Also, with the Hyperion, the wiring is squeezed between the front and side panels, which could cause chafing. Is it that way with the Broan? I'm not an engineer, but it sure looks like Trane forget to include wire grommets when they designed the cabinet, to me, anyway. And with the sheer size of the Hyperion, I'm afraid all the piping coming out the front of the a/h may get in the way of my utility room door opening up against the a/h stand. It currently opens a full 90 degrees and I would be upset if I had to squeeze through a 75 degree opening between the door and my laundry equipment (dryer). Any comments on the a/h setup?
    Delaware
    Florida Space Coast
    I believe this confirms what SkyHeating said in his comments. If there's more to it than that, I'm not seeing it in the link you provided.
    I have installed 2 iq drive systems. Both of them we have installed all new ductwork. Both customers are ecstatic about the system and utilities have dropped very significantly. The unit varies anywhere from 30%-118%. They rarely shut completely off and maintain very good humidity levels and comfort throughout the house. These types of units are where the hvac industry is heading. Soon all manufacturers will be rolling out a variable speed line.
    Quote Originally Posted by Florida Joy View Post
    Is your home leaky? Ducts? Static pressure?
    Florida Space Coast
    Duct Leakage & Infiltrometer Reports
    I'm attaching the Duct Leakage Flow Hood Report and the Infiltrometer Report.
    Static pressure wasn't a number that was shared with me, unless it's in one of these reports.
    Duct Leakage Report.pdf
    Infiltrometer Report.pdf