    Quote Originally Posted by coolwhip View Post
    Whoever did that venting had their head up their flue.
    Especially with an induced draft, if the vent ever gets partially plugged it gets to vent at the water heater.

    Even with the old school draft box, if we did that there would be a good rise and also a Y not a T, that needs to be corrected soon, it's an accident waiting to happen.

    Also we never set a furnace down into the drain pan, we jack it up some to keep the water from being drawn into the blower it "will" seep through that bottom door, the suction will draw it in.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  2. #15
    Join Date
    Dec 2011
    Location
    Twin Cities Minnesota
    Posts
    223
    Is that a "copper fitting" in the W.H. gas piping line ?

  3. #16
    Join Date
    Jul 2009
    Location
    WV
    Posts
    17
    Isn't the water heater supposed to be vented before the furnace ?

  4. #17
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    1,694
    I thought that in apartments you were supposed to install the water heater in front of the furnace. That's how I see them here.


  5. #18
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    The water heater and furnace on a common vent is acceptable per code.

    The orientation of the tee is NOT acceptable.
    If more government is the answer, then it's a really stupid question.

  6. #19
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    2,901
    Quote Originally Posted by mark beiser View Post
    The water heater and furnace on a common vent is acceptable per code.

    The orientation of the tee is NOT acceptable.
    Mark is correct.

    Even though an induced draft and h2o heater common vented is acceptable in the code book I bet we(meaning HVAC techs seeing it in the field) could have a good argument that the code book is behind on the times. Maybe I'll start a thread ; ).

    The way this is vented is def wrong wether it's passed inspection or not, the common vents that seem to work are when the units tie into a vertical Y fitting and it's run with B vent.

    This next part is for others, not mark : ).

    An induced draft 80% unit is rated as a category 1 appliance just like a natural draft water heater, meaning it uses stack effect/ natural draft after the inducer same as the h2o heater, once physics takes effect(properly run and tied together of course) both flues are in a negative pressure.

    Hopefully the code will get updated someday and because these setups are inviting problems, like spillage on the h2o heater when the furnace starts up but apparently some doses of flue gases are not a concern : /...

  7. #20
    Join Date
    May 2006
    Posts
    373
    You don't energize a gas line thats power
    You presserize a gas line

  8. #21
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    4,923
    Quote Originally Posted by Mr Bill View Post
    Is that even legal? I have never in over 35 years seen that, but I know each local does things a little different. In Houston the inspector would probably ticket you for being on crack.
    Nope.
    You always have to discharge to a place that is clear there is a problem. Tying into a condensate line, you'd never know if it pop'd in the summer.

    Although this may be boiler only code, you can not have more than (3) 90's in the discharge, and you can never gang them with other discharge lines.


    The problem is that pop off valves are a warning that goes unnoticed, even though it's indicating unsafe operation.
    As I type this, my I'm missing an expansion tank on my water heater, and there's always a little puddle under mine XD
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  9. #22
    Join Date
    Dec 2011
    Location
    Northeast PA
    Posts
    209
    nice expansion tank
    O wait yea lacking that too.

  10. #23
    Join Date
    Oct 2011
    Location
    Toronto
    Posts
    35
    I can't believe this... A condo full of these? I think a license should be revoked

  11. #24
    I don't get how some people can live with themselves...that is an obvious "deadhead" flue connection. Surprised people did not suffer some degree of respiratory distress.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event