01-28-2013, 09:36 AM #14
Especially with an induced draft, if the vent ever gets partially plugged it gets to vent at the water heater.

Even with the old school draft box, if we did that there would be a good rise and also a Y not a T, that needs to be corrected soon, it's an accident waiting to happen.
Also we never set a furnace down into the drain pan, we jack it up some to keep the water from being drawn into the blower it "will" seep through that bottom door, the suction will draw it in.“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
01-30-2013, 08:20 AM #15
Professional Member*
- Join Date
- Dec 2011
- Location
- Twin Cities Minnesota
- Posts
- 114
Is that a "copper fitting" in the W.H. gas piping line ?
-
01-30-2013, 09:39 AM #16
Regular Guest
- Join Date
- Jul 2009
- Location
- WV
- Posts
- 13
Isn't the water heater supposed to be vented before the furnace ?
-
01-30-2013, 10:01 AM #17
I thought that in apartments you were supposed to install the water heater in front of the furnace. That's how I see them here.
-
01-30-2013, 10:24 AM #18
The water heater and furnace on a common vent is acceptable per code.
The orientation of the tee is NOT acceptable.If more government is the answer, then it's a really stupid question.
-
01-30-2013, 10:46 AM #19
Mark is correct.
Even though an induced draft and h2o heater common vented is acceptable in the code book I bet we(meaning HVAC techs seeing it in the field) could have a good argument that the code book is behind on the times. Maybe I'll start a thread ; ).
The way this is vented is def wrong wether it's passed inspection or not, the common vents that seem to work are when the units tie into a vertical Y fitting and it's run with B vent.
This next part is for others, not mark : ).
An induced draft 80% unit is rated as a category 1 appliance just like a natural draft water heater, meaning it uses stack effect/ natural draft after the inducer same as the h2o heater, once physics takes effect(properly run and tied together of course) both flues are in a negative pressure.
Hopefully the code will get updated someday and because these setups are inviting problems, like spillage on the h2o heater when the furnace starts up but apparently some doses of flue gases are not a concern : /...
-
01-31-2013, 03:50 AM #20
Regular Guest
- Join Date
- May 2006
- Posts
- 309
You don't energize a gas line thats power

You presserize a gas line
-
01-31-2013, 07:22 PM #21
Nope.
You always have to discharge to a place that is clear there is a problem. Tying into a condensate line, you'd never know if it pop'd in the summer.
Although this may be boiler only code, you can not have more than (3) 90's in the discharge, and you can never gang them with other discharge lines.
The problem is that pop off valves are a warning that goes unnoticed, even though it's indicating unsafe operation.
As I type this, my I'm missing an expansion tank on my water heater, and there's always a little puddle under mine XD"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
01-31-2013, 07:49 PM #22
Professional Member
- Join Date
- Dec 2011
- Location
- Northeast PA
- Posts
- 202
nice expansion tank

O wait yea lacking that too.
-
02-01-2013, 02:30 PM #23
Regular Guest
- Join Date
- Oct 2011
- Location
- Toronto
- Posts
- 29
I can't believe this... A condo full of these? I think a license should be revoked
-
02-01-2013, 04:54 PM #24
Regular Guest
- Join Date
- Jan 2013
- Posts
- 954
I don't get how some people can live with themselves...that is an obvious "deadhead" flue connection. Surprised people did not suffer some degree of respiratory distress.