    delta rts406

    Can anyone tell me it there is replacement zone sensor, I've haven't been able to get any information from delta controls, it seems its a big secret to them they wouldn't even respond by email or phone?

  2. #2
    Join Date
    Oct 2009
    Location
    Nova Scotia, Canada
    Posts
    172
    Use a RTS-424. It looks like the new BACStats. But be careful. You need to change the power from 8vdc to 24vac or smoke comes out.
    Follow me @blankscole

  3. #3
    Join Date
    Feb 2011
    Location
    Texas
    Posts
    5
    CE-TECH thanks for replying Iam in the San Antonio area would you now ware I could get a replacement sensor, I called the Dallas delta controls thy say there is not any delta controls here. Would the voltages change be done at the controller or would that be a auxiliary power connection needed, could I use a different brand sensor since it says back net on sensor with 8Vdc power . Is is possible to use a brand like automated logic?