    Have any of you guys had any issues using stay bright solder on glycol systems? I cannot find if you can use it on chilled water with glycol. I have a customer asking me to give him a speck sheet showing you can use on a glycol system.
    If you find it bad 3 different ways- ~its bad~

  2. #2
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    675
    Post Likes
    I have used it a lot on chilled water and heating water systems that have glycol in the water. What concerns do you have?

  3. #3
    Join Date
    Jan 2004
    Posts
    169
    Post Likes
    Thread Starter
    Quote Originally Posted by hands View Post
    I have used it a lot on chilled water and heating water systems that have glycol in the water. What concerns do you have?
    I was told today by a technician that glycol eats the silver and will come apart after a couple years and I have never heard that. He said they had a bulding they had to redo because of this issue. I have not ever heard of this and I tried to find it on line but could not find you can or can't.
    If you find it bad 3 different ways- ~its bad~

  4. #4
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,011
    Post Likes
    Hope I am not going off topic. Many years ago we used water in the summer in car radiators. Come winter we put the antifreeze (glycol), back in
    it was common to find a new leak in the radiator or heater core. We won't get into "non-permanent" antifreeze. I am dating myself.

  5. #5
    Join Date
    Dec 2012
    Location
    Spokane, Washington
    Posts
    135
    Post Likes
    I call BS on this....I've done numerous heated driveway and sidewalk jobs that are still working 12+ years later and the manifold and flat plate hx were done with stay brite. If you "dig up" something, I'd like to see it.

  6. #6
    Join Date
    Dec 2006
    Location
    new england
    Posts
    751
    Post Likes
    I've worked on numerous chilled water and hot water hydronic systems with high glycol concentrations. I call BS too.
    Chaos equals cash$$$

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    13,928
    Post Likes

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,813
    Post Likes
    Quote Originally Posted by teckster View Post
    Have any of you guys had any issues using stay bright solder on glycol systems? I cannot find if you can use it on chilled water with glycol. I have a customer asking me to give him a speck sheet showing you can use on a glycol system.

    Your co-workers are partially right, pure glycol will attack silver joins and the heat transfer loop as a whole, thats why in HVAC we use "inhibited glycol", basically the glycol comes mixed with corrosion inhibitors that keep the solution from reacting with oxygen and turning acidic.

  9. #9
    Join Date
    Jan 2004
    Posts
    169
    Post Likes
    Thread Starter
    Thank you guys for all your answers and I am going to send the coupler that came to a lab to be tested as all the piping is over a brand new class 7 clean room and we don't want to take any chances. The piping was installed four years ago and I want to be sure we are not having a reaction with the glycol. I will also pull a sample and have it tested to ensure it is not acidic.
    If you find it bad 3 different ways- ~its bad~

  10. #10
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    if it attacks the silver then you would not be able to use any of the common solders use for joining copper together most all of it is 5, 10, 15 , 45,95% silver im thinking BS too

  11. #11
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    there would be alot of chiller barrells failing inside with glycol running in them

  12. #12
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,813
    Post Likes
    one of our customers is a foundry that makes parts for the aerospace industry, the steel presses are kept cool by two motiv-air chillers and a large glycol loop, years ago they were rebuilding one press and lost couple hundred gallons of glycol,maintenance guys got a hold of uninhibited, pure glycol and pumped the loop with it, time went by and leaks starting to show everywhere, finally at the chiller barrel, we got called in a little too late.

  13. #13
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,614
    Post Likes
    Pure quill glycol isn't good for all chilled water systems. I always used treated glycol. Rust inhibitors, and also touted as containing a chemical that was good for valves and pumps. According to the sales people.
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.