    OROAB 5-210 R407C on Liebert Remote Condenser.

    OAT 8*. head pressure control making a loud vibrating noise. Is this a sign of internal damage to the valve or diaphram or is it common at this low of ambients

  2. #2
    Join Date
    Jun 2009
    Location
    Garland, TX
    Posts
    362
    I have no experience with that particular valve, but two of my supervisors have told me of instances where a ridiculously loud noise was found to be coming from a headmaster.

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    I would say yes. Have seen it once on a Hoshizaki IM. Replaced valve, noise is gone.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  4. #4
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    331
    i've heard noise come from them on start up or pump down, what is the discharge and liquid pressures at?

  5. #5
    Join Date
    Jun 2006
    Location
    midwest
    Posts
    107
    Just shut down ckt 1, to dang cold out with windchill at -17* f. Will return at end of week to investigate. Customer happy and occupants in office below condenser happy with noise gone .