OROAB 5-210 R407C on Liebert Remote Condenser.
OAT 8*. head pressure control making a loud vibrating noise. Is this a sign of internal damage to the valve or diaphram or is it common at this low of ambients
-
01-26-2013, 09:05 PM #2
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 362
I have no experience with that particular valve, but two of my supervisors have told me of instances where a ridiculously loud noise was found to be coming from a headmaster.
-
01-27-2013, 01:06 AM #3
I would say yes. Have seen it once on a Hoshizaki IM. Replaced valve, noise is gone.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-27-2013, 01:14 AM #4
Professional Member*
- Join Date
- Nov 2009
- Location
- Richmond, working under tarps
- Posts
- 331
i've heard noise come from them on start up or pump down, what is the discharge and liquid pressures at?
-
01-27-2013, 10:33 AM #5
Regular Guest
- Join Date
- Jun 2006
- Location
- midwest
- Posts
- 107
Just shut down ckt 1, to dang cold out with windchill at -17* f. Will return at end of week to investigate. Customer happy and occupants in office below condenser happy with noise gone .