Thread: Jace 6 or 7?
-
01-24-2013, 11:55 AM #1
Jace 6 or 7?
I am trying to decide which Jace to go with and need some help deciding.
I will be controlling 18 AI, 10 AO, 18 BO, and 15 BI through logic on the jace. Besides that I will be importing points from 2 boilers and a chiller over MS/TP.
The real reason I'm considering the 700 though is that I will have 35 EasyIO 30P's, which are stand alone controllers. Each one controlling an air handler. I will be importing all these points into the Jace through Sedona and have graphics for them all. I don't know how much RAM it will take to keep up with all communications.
What is your guys thoughts on this?
-
01-25-2013, 02:13 AM #2
if yr using Bacnet IP for the EasyIOs then gut-feeling says a 600 should romp it in.
if yr doing MSTP then ...er...maybe not...depends1 + 1 = 3 ( *** for very large values of 1)
...everybody wants a box of chocolates and long stemmed rose
-
01-31-2013, 11:00 AM #3
I will be using tcom to communicate with the 30P's which is the essentially using Sedona, this way every point is accessible in the Jace. I will also be eliminating all NDIO/NRIO and moving everything to 30P's so the chiller and boiler plants will be standalone.
Does anyone have experience with a large system like this?
-