Results 1 to 9 of 9

Thread: Furnace not lighting/Gas line freezing?

  1. #1
    Join Date
    Jan 2013
    Posts
    3
    Post Likes

    Furnace not lighting/Gas line freezing?

    Came home from work last night to find that the heat had stopped working on the coldest day of the season. (20's all day, 1/4" of freezing rain/sleet fell)

    Unit is an outdoor Trane furnace/AC "all in one", natural gas. It was installed in 2006, and had never been serviced.

    Luckily, the one HVAC guy that answered his phone happened to be a few miles away, he came out at around 8PM, despite the bad road conditions.

    The gas valve seemed to be bad, so he swapped in a new one. No improvement, gas wasn't getting to the valve. He then got a torch and warmed up the regulator, which happens to next to the unit, exposed to the weather, and the black plastic cap had popped off (months ago) and was sitting nearby. That got gas flowing to the valve, but it still didn't light. Turns out he put the valve in backwards, so he reinstalled. (obviously he'd had a long day)

    Now the gas would light, but wouldn't stay lit. He checked the flame sensor, and it had white residue on it, so he cleaned it off...still nothing. This particular unit has two...burners (?), one has the flame sensor and the other has the ignitor. he said the channel between the two was dirty, so the flame from the lit burner wouldn't get over to light the other.

    After all this, everything seemed to work. House was warm until I went to bed, but I woke up to a cold house.

    It's still cold outside, roads are still icy, etc.

    The only thing I felt comfortable doing myself was to cycle the power...no ignition. I took a hair dryer to the regulator, and tried again. Furnace has been on for about an hour now, hasn't turned off since the house is still cold.


    I'm left wondering what the original problem was...the valve, or the regulator, or a combination of several things? The problem doesn't seem to be fixed, should I go back to the original repair guy, or find someone else? What should I request that he do? Do regulators "go bad"? Should I do something to keep it warm, maybe heat tape or...? Could there be moisture trapped within the regulator?

    Thanks!

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Have them replace the regulator and route it under the house do it won't be exposed to the elements then run pipe out of crawl and to unit. I've had to do this a few times.

  3. #3
    Join Date
    May 2007
    Location
    Alabama
    Posts
    911
    Post Likes
    Quote Originally Posted by kram13 View Post
    Came home from work last night to find that the heat had stopped working on the coldest day of the season. (20's all day, 1/4" of freezing rain/sleet fell)

    Unit is an outdoor Trane furnace/AC "all in one", natural gas. It was installed in 2006, and had never been serviced.

    Luckily, the one HVAC guy that answered his phone happened to be a few miles away, he came out at around 8PM, despite the bad road conditions.

    The gas valve seemed to be bad, so he swapped in a new one. No improvement, gas wasn't getting to the valve. He then got a torch and warmed up the regulator, which happens to next to the unit, exposed to the weather, and the black plastic cap had popped off (months ago) and was sitting nearby. That got gas flowing to the valve, but it still didn't light. Turns out he put the valve in backwards, so he reinstalled. (obviously he'd had a long day)

    Now the gas would light, but wouldn't stay lit. He checked the flame sensor, and it had white residue on it, so he cleaned it off...still nothing. This particular unit has two...burners (?), one has the flame sensor and the other has the ignitor. he said the channel between the two was dirty, so the flame from the lit burner wouldn't get over to light the other.

    After all this, everything seemed to work. House was warm until I went to bed, but I woke up to a cold house.

    It's still cold outside, roads are still icy, etc.

    The only thing I felt comfortable doing myself was to cycle the power...no ignition. I took a hair dryer to the regulator, and tried again. Furnace has been on for about an hour now, hasn't turned off since the house is still cold.


    I'm left wondering what the original problem was...the valve, or the regulator, or a combination of several things? The problem doesn't seem to be fixed, should I go back to the original repair guy, or find someone else? What should I request that he do? Do regulators "go bad"? Should I do something to keep it warm, maybe heat tape or...? Could there be moisture trapped within the regulator?

    Thanks!
    Use a torch on a GAS regulator??? Even a long day does not account for putting a gas valve in backwards. There are a number of possibilities. You need to make another phone call.

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    where is the regulator at? if it is main one feeding the house next to the gas meter is is your utility companies problem and they need to be called.

    if it is right near the unit it is your problem and you will have to get it replaced.
    probably nothing wrong with the gas valve that was replaced............twice.

  5. #5
    Join Date
    Jan 2013
    Posts
    3
    Post Likes
    Thread Starter
    The regulator is just upstream from the unit. I texted (!) the guy and he put in a new regulator...hopefully that takes care of it. He didn't charge anything, so that's a plus...though his helper was smoking during the process, which seemed odd.

    I'm reluctant to pay for the regulator to be relocated considering it hasn't been an issue for 7 years... Would some sort of cover (other than the plastic cap) to keep the ice/snow away suffice?

  6. #6
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    They make a cover for them to keep the elements out but still let them breath. The vent cap being broke off is what caused the problem {the plastic piece}it let water in to the regulator. "NEVER USE A TORCH ON A REGULATOR"

  7. #7
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,504
    Post Likes
    and never put a regulator in a confined space without venting the relief to the outside

  8. #8
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes
    Quote Originally Posted by kram13 View Post
    The regulator is just upstream from the unit. I texted (!) the guy and he put in a new regulator...hopefully that takes care of it. He didn't charge anything, so that's a plus...though his helper was smoking during the process, which seemed odd.

    I'm reluctant to pay for the regulator to be relocated considering it hasn't been an issue for 7 years... Would some sort of cover (other than the plastic cap) to keep the ice/snow away suffice?
    Never allow service people to smoke in your home. If they must smoke, tell them to sit in their vehicle.

    A torch on a gas regulator is a guy looking to make headlines.

    If an outdoor regulator froze up, contact the utility about replacement and sizing. Inspect and measure all your gas lines to ensure proper sizing. If you have a Medium Pressure regulator indoors near the equipment, have another pro ensure it is installed to code with a shutoff immediately upstream, a sediment trap to protect it and a means of measuring outlet pressure. As noted, if in a confined space, the vent must be routed to the outdoors.

    If the protective cap is off the outdoor regulator it must be replaced ASAP. If ice gets in there, it can damage the reg. Call the utility.

  9. #9
    Join Date
    Jan 2013
    Posts
    3
    Post Likes
    Thread Starter
    Quote Originally Posted by hearthman View Post
    Never allow service people to smoke in your home. If they must smoke, tell them to sit in their vehicle.

    A torch on a gas regulator is a guy looking to make headlines.

    If an outdoor regulator froze up, contact the utility about replacement and sizing. Inspect and measure all your gas lines to ensure proper sizing. If you have a Medium Pressure regulator indoors near the equipment, have another pro ensure it is installed to code with a shutoff immediately upstream, a sediment trap to protect it and a means of measuring outlet pressure. As noted, if in a confined space, the vent must be routed to the outdoors.

    If the protective cap is off the outdoor regulator it must be replaced ASAP. If ice gets in there, it can damage the reg. Call the utility.
    He was outside, as was the unit and regulator. Again, the regulator is just upstream from the unit, down from a cutoff and and a trap, not the gas companies problem. The cutoff was off when he was heating it with the torch, still seemed a bit odd though.

    Someone should come up with a better designed regulator that doesn't depends on a flimsy plastic cap to keep it functional...

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •