    Motor FLA

    Hello everyone,

    I came across an FLA listed like this on a motor today: 4/2-2 FLA
    I understand what FLA means, but haven't encountered it written this way before. What does it mean when written this way? Thanks very much.

  2. #2
    Join Date
    Nov 2008
    Location
    Long Island NY
    Posts
    169
    Is it a dual voltage motor?

    Sent from my SGH-I777

  3. #3
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    Im guessing it is a dual voltage motor if you are using the lower voltage it will be the higher amperage and for the higher voltage it would be the lower amperage

  4. #4
    It's a possibility. I think it was from a rooftop exhaust fan motor. I looked at so much equipment today, I don't remember for sure what motor had this FLA. I'm just going by what I wrote on my notepad: "4/2-2 FLA?"

  5. #5
    Quote Originally Posted by brian.cornell View Post
    Im guessing it is a dual voltage motor if you are using the lower voltage it will be the higher amperage and for the higher voltage it would be the lower amperage
    So can you break down what the numbers, slashes, and dashes mean? Thanks!

  6. #6
    Join Date
    Feb 2013
    Location
    Florida
    Posts
    69
    Dual voltage motors have the fla at each voltage separated by a slash. I'm not really sure what the -2 is about

  7. #7
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    Im not sure about thhe -2 part either

  8. #8
    Join Date
    Jan 2012
    Location
    California
    Posts
    81
    More than likely 4 / 2.2 for a dual voltage motor.

  9. #9
    Quote Originally Posted by catalina_mike View Post
    More than likely 4 / 2.2 for a dual voltage motor.
    That would make sense. Why does it seem like we're always running into things like this in this industry? On top of everything else, now we have to worry about manufacturers using dashes for periods. Don't even get me started on using spell check before they print user manuals.

  10. #10
    Join Date
    Dec 2006
    Location
    new england
    Posts
    587
    120vac=4 amps
    208vac=2.2 amp
    Not positive on the voltage above, but next time your on a roof check out some motor nameplates and this will all make sense.
    Chaos equals cash$$$

  11. #11
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    441
    Quote Originally Posted by HVAC_Austin View Post
    Hello everyone,

    I came across an FLA listed like this on a motor today: 4/2-2 FLA
    I understand what FLA means, but haven't encountered it written this way before. What does it mean when written this way? Thanks very much.
    What was the voltage? It could be something like 208/240-460 :volt and 4/2-2 amp. That's 208 volt, 4 amp. 240 volt, 2 amp. 460 volt, 2 amp.

  12. #12
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,006
    Quote Originally Posted by hands View Post
    What was the voltage? It could be something like 208/240-460 :volt and 4/2-2 amp. That's 208 volt, 4 amp. 240 volt, 2 amp. 460 volt, 2 amp.
    that doesn't really add up but i was thinking along the same lines

    120/208-230 VAC......without any decimals 208 and 230 volt units would draw about the same amps.
    It's tube brushing season...93% done (39.35 miles of tubing)...only 1,242 tubes to go!

    Original member of the Raccoon Brotherhood.

    EVERYTHING IS AWESOME!!!

  13. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    1,864

    Motor FLA

    Quote Originally Posted by fitzyfitta View Post
    120vac=4 amps
    208vac=2.2 amp
    Not positive on the voltage above, but next time your on a roof check out some motor nameplates and this will all make sense.
    This brings to mind a question ive been wandering for a while. I know in a resistive load if volts go up amps go up as well, is this opposite for a inductive load ?I see people going both ways with it here.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event