Thread: RTU burner cutting in and out
-
01-25-2013, 02:54 PM #1
New Guest
- Join Date
- Jan 2013
- Posts
- 4
RTU burner cutting in and out
Unit: Lennox GCS16-411-100-1P Packaged rooftop
So the burner on this rooftop unit keeps cutting in and out when it first starts. I inspected the heat exchanger for any holes but didn't see any; although the style of heat exchanger makes it difficult to fully inspect.
As soon as the flame drops out the ignitor fires again and the burner lights so the flame sensor is working correctly. Voltage is continuous to the gas valve through all of this so its not the ignition module.
I put my manometer on the outlet of the gas valve but naturally I couldn't reproduce the problem at that point. The customer says the unit will run for a while and then lockout and then eventually come back on.
Im wondering if the flame is getting blown out by something (the building is on the shore of Lake Ontario and its been very bad weather lately) or if the gas valve is having trouble staying open despite proper voltage.
Hazard a guess.
Heres a link to a video of the problem. http://s38.beta.photobucket.com/user...e26ae.mp4.html
-
01-25-2013, 05:11 PM #2
I think this one is more for the pro technical forum.
-
01-25-2013, 10:01 PM #3
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
nice rifle
-
01-25-2013, 11:04 PM #4
Professional Member
- Join Date
- Nov 2012
- Location
- Macomb Twp MI
- Posts
- 44
Nice video, or random pics of you and chicks, whichever.
-
01-26-2013, 10:20 AM #5
Is that a Catilina or Bonneville?
Might want to change your photobucket settings to "private"Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-26-2013, 10:37 AM #6
Professional Member
- Join Date
- Feb 2012
- Location
- Durham, NC
- Posts
- 64
One sick photobucket account
-
01-26-2013, 02:18 PM #7
Regular Guest
- Join Date
- Feb 2012
- Location
- Tyler, Tx
- Posts
- 11
Gonna have to check gas pressure. If that checks out pull it apart to check exchanger.
-
01-27-2013, 01:54 PM #8
Professional Member
- Join Date
- May 2000
- Location
- Salem, WI US
- Posts
- 43
Check flame signal and gas pressures. I have had momentary voltage drops at the wiring connection on limits cause this scenario as well.
Beta
-
01-28-2013, 11:09 AM #9
New Guest
- Join Date
- Jan 2013
- Posts
- 4
Its a Grandville actually. Same thing though. I haven't used that photobucket account in ages hence all the BS in there.
Every time I connect a manometer I cant reproduce the problem. It appears if the flame is going out, then the flame sensor is seeing it and restarting the ignitor and not the other way around which means the flame is going out from an outside source, so to speak, rather than being shut off from flame failure.
I guess i'll have to start changing some parts if i can't get the gas pressure to check out.
-
01-28-2013, 11:28 AM #10
You said you checked the voltage to the gas valve while this is happening. Did the voltage fluctuate when this was happening? I'm wondering if the gas valve coil is bad and dropping in and out. If so, you should see a voltage fluctuation. If the gas valve is good I would suspect something is disrupting the flame. HX, inducer, wind sheer.....etc. You said the weather has been bad. Perhaps something temperature related.
"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-28-2013, 11:38 AM #11
New Guest
- Join Date
- Jan 2013
- Posts
- 4
I didn't really see voltage fluctuation but it happens so quick and my meter doesn't respond instantly, especially in -25C. There is no pilot on this so it just opens the valve and starts the ignitor when it sees flame failure and its only a fraction of a second between dropout and reignition so its really hard to figure out where its coming from. I think i'll just see about switching the gas valve out with something I have laying around to eliminate that possibility.
-
01-28-2013, 11:43 AM #12"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-28-2013, 11:44 AM #13
Wow. I had forgotten about the Grandville.
Are you seeing any variance in the flame rectification current prior to the unit trying to restart?


Reply With Quote