    Discharge pressure on ice machine?

    According to the maunal on my Scotsman 1356 the discharge pressure should be 245. Now is that all the time or when it going through a freeze or a harvest cycle? I've been trying to adjust it but it keeps kicking out on high pressure overload.

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    not sure on scotsman but most of the time when IM manufacturers list operating pressures it is 5-10 minutes into freeze cycle.

  3. #3
    Join Date
    Sep 2007
    Location
    Denver , Co.
    Posts
    109
    Post Likes
    water cooled or air cooled , Man i remember a couple years ago Scotsman had issues with the dist. tubes coming off TXV , causing uneven ice forms and high head , if its a remote ,
    check your gas level a lot of guys don't realize that those units are charged at factory they install and start dumping 404a into line sets , as far as pressure with fan cycling or water reg valve
    you should have operating temp fairly quick

    Ice V
    Outlaw guns? only outlaws will have guns
    Those who live by the sword are SHOT by us who don't.

  4. #4
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    95
    Post Likes
    Thread Starter
    Ice,

    Sorry it is water cooled. That's what I'm talking about is the regulator that adjusts the water pressure going through the condenser. The amount of water flow adjusts the head pressure. I need to adjust it so its at 245 but not sure at what point in the procedure it needs to run at 245. Hope I'm making since.

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Water-cooled machines will typically run at the same discharge pressure all the time because the water regulating valve controls the pressure. If the supply water temperature is too high or the available pressure is too low, then of course, even a wide open regulating valve won't help.

    To set the pressure at 245 psig, I recommend adjusting to a slightly higher pressure like 260 psig or so, and then slowly dial down to 245 psig.

    Also...It's a good idea to do this about 5 minutes into the freeze cycle.

  6. #6
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    What is the discharge pressure doing? Steady? Steady climb? Hunting up and down? What pressure is it tripping at? Back valve way off before you start the machine and evaluate. Is water coming out hot, warm, or cool? Need to gather some more info to lead us to the actual problem.

  7. #7
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    245# is the setting for freeze cycle

  8. #8
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    95
    Post Likes
    Thread Starter
    It wasn't harvesting. It wasn't getting a high enough head pressure when the hot gas valve opened, hence not hot enough gas, to break the ice off the evaporator. I was trying to set the water pressure regulator but I don't think my charge is right to get it where I need it. Let's just say there's been a lot of hands in this machine before they came to me. We have a lot of guys here that have the attitude if its not running right I must need a shot of freon!!

  9. #9
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Confused now. Tripping on high head but not high enough head to harvest?

  10. #10
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    204
    Post Likes
    What pressure is it cutting out at.

    Sent from my SGH-T999 using Tapatalk 2

  11. #11
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    95
    Post Likes
    Thread Starter
    When I wasn't high enough I was trying to set it and no matter where I set it it was tripping out. That's why I was asking at what point in the sequence I needed to set it. Also that's why I'm thinking my charge may be off. Hope I'm making sense here.

  12. #12
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    204
    Post Likes
    How long into the cycle did it trip? Did you check amps?.. are you sure its tripping on high head. Usually you will see on most units that high head will cut off at around 300 or above.. so definitely double check what your tripping on and at what pressure...

    Sent from my SGH-T999 using Tapatalk 2

  13. #13
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Don't know if charge is the issue or not. Easy to know for sure. Pull it. Weigh it and see. Evacuate and weigh correct charge in. I would do alittle more checking first though. Find out what it actually tripping and why. Is it HP or comp internal OL? Still alittle confused with the info provided.

  14. #14
    Join Date
    Apr 2001
    Location
    MINN
    Posts
    947
    Post Likes
    could be non condensible or mixed refrigerants???

  15. #15
    Join Date
    Nov 2010
    Location
    Missouri
    Posts
    401
    Post Likes
    Quote Originally Posted by beb View Post
    could be non condensible or mixed refrigerants???
    I`ll second that.

  16. #16
    Join Date
    Feb 2007
    Location
    Northern NJ
    Posts
    829
    Post Likes
    On water cooled machines, the first thing I look at when they don't harvest is the water regulating valve. Often especially in hard water areas, the valve seat will clog with minerals and not seat all the way. It is essential that water flow stop during harvest to allow heating of gas. A sure fire way of testing is to valve off water flow to condenser during harvest. If it drops valved off but doesn't when valve is open, you need a new water regulating valve.

  17. #17
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    95
    Post Likes
    Thread Starter
    Another question on this issue. If the valve is bad, is there a way I can isolate the refrigerant in the system so I can change it without evacuating the whole system?

  18. #18
    Join Date
    Jun 2012
    Location
    Tenn
    Posts
    167
    Post Likes
    Quote Originally Posted by mwright View Post
    Another question on this issue. If the valve is bad, is there a way I can isolate the refrigerant in the system so I can change it without evacuating the whole system?

    You can change the water discharge valve without recovering the refrigerant. I feel as I should mention, however, that if you suspect that the system is overcharged, you need to ensure that you have a correct charge. Then you adjust the water discharge valve. If you ensure that you have proper charge and correct water out pressure and continue to have the unit tripping on high discharge pressure, your next step is to clean the scale off the water side of the condensor.

  19. #19
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    95
    Post Likes
    Thread Starter
    The pressure regulator is bad. Doesn't matter how you adjust it it is wide open. So I need to replace it and don't want to evacuate it.

  20. #20
    Join Date
    Jun 2012
    Location
    Tenn
    Posts
    167
    Post Likes
    Quote Originally Posted by mwright View Post
    The pressure regulator is bad. Doesn't matter how you adjust it it is wide open. So I need to replace it and don't want to evacuate it.

    You should be able to secure the water and replace the valve.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •