Discharge pressure on ice machine?
According to the maunal on my Scotsman 1356 the discharge pressure should be 245. Now is that all the time or when it going through a freeze or a harvest cycle? I've been trying to adjust it but it keeps kicking out on high pressure overload.
01-25-2013, 12:58 PM #2
not sure on scotsman but most of the time when IM manufacturers list operating pressures it is 5-10 minutes into freeze cycle.
01-25-2013, 01:46 PM #3
water cooled or air cooled , Man i remember a couple years ago Scotsman had issues with the dist. tubes coming off TXV , causing uneven ice forms and high head , if its a remote ,
check your gas level a lot of guys don't realize that those units are charged at factory they install and start dumping 404a into line sets , as far as pressure with fan cycling or water reg valve
you should have operating temp fairly quick
Ice VOutlaw guns? only outlaws will have guns
Those who live by the sword are SHOT by us who don't.
01-25-2013, 02:32 PM #4
- Feb 2012
- Savannah, NY
- 67
Ice,
Sorry it is water cooled. That's what I'm talking about is the regulator that adjusts the water pressure going through the condenser. The amount of water flow adjusts the head pressure. I need to adjust it so its at 245 but not sure at what point in the procedure it needs to run at 245. Hope I'm making since.
01-25-2013, 06:19 PM #5
Water-cooled machines will typically run at the same discharge pressure all the time because the water regulating valve controls the pressure. If the supply water temperature is too high or the available pressure is too low, then of course, even a wide open regulating valve won't help.
To set the pressure at 245 psig, I recommend adjusting to a slightly higher pressure like 260 psig or so, and then slowly dial down to 245 psig.
Also...It's a good idea to do this about 5 minutes into the freeze cycle.
01-25-2013, 07:30 PM #6
What is the discharge pressure doing? Steady? Steady climb? Hunting up and down? What pressure is it tripping at? Back valve way off before you start the machine and evaluate. Is water coming out hot, warm, or cool? Need to gather some more info to lead us to the actual problem.
01-25-2013, 08:11 PM #7
- Jun 2009
- Garland, TX
- 349
245# is the setting for freeze cycle
01-25-2013, 08:14 PM #8
- Feb 2012
- Savannah, NY
- 67
It wasn't harvesting. It wasn't getting a high enough head pressure when the hot gas valve opened, hence not hot enough gas, to break the ice off the evaporator. I was trying to set the water pressure regulator but I don't think my charge is right to get it where I need it. Let's just say there's been a lot of hands in this machine before they came to me. We have a lot of guys here that have the attitude if its not running right I must need a shot of freon!!
01-25-2013, 09:18 PM #9
Confused now. Tripping on high head but not high enough head to harvest?
01-25-2013, 09:25 PM #10
What pressure is it cutting out at.
Sent from my SGH-T999 using Tapatalk 2
01-25-2013, 09:27 PM #11
- Feb 2012
- Savannah, NY
- 67
When I wasn't high enough I was trying to set it and no matter where I set it it was tripping out. That's why I was asking at what point in the sequence I needed to set it. Also that's why I'm thinking my charge may be off. Hope I'm making sense here.
01-25-2013, 10:06 PM #12
How long into the cycle did it trip? Did you check amps?.. are you sure its tripping on high head. Usually you will see on most units that high head will cut off at around 300 or above.. so definitely double check what your tripping on and at what pressure...
01-26-2013, 12:41 PM #13
Don't know if charge is the issue or not. Easy to know for sure. Pull it. Weigh it and see. Evacuate and weigh correct charge in. I would do alittle more checking first though. Find out what it actually tripping and why. Is it HP or comp internal OL? Still alittle confused with the info provided.