Morning guys, Trane package unit had me scratching my head.
Trane 3ton RTU YCD036C4LOBE manufactured 1/2001
Symptoms: IDFM keeps running, T-stat NOT calling for heat/cooling/fan
Trouble shoot: Identical unit on the roof so I swapped out t-stat, control module, ignition module, inclosed IDFM contacter, removed spade connector to the high limit inside the heat exchanger and IDFM compartment.
Any Ideas?
01-25-2013, 09:29 AM #2
Common problem. Windings are shorted.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
01-25-2013, 09:41 AM #3
- Aug 2012
- Los Angeles
- 18
really??? when the IDFM contactor is de-energized by manually removing 24v leg, motor stops running.
In other words IDFM contactor is constantly energized.
01-25-2013, 09:42 AM #4
Get pro status and ask in Pro Commercial. We can tell you all about it.
01-25-2013, 09:44 AM #5
- Aug 2012
- Los Angeles
- 18
Trying to get there, few more posts to go.
01-25-2013, 02:20 PM #6
New Guest
- Jan 2013
- 4
Well the contactor can only be energized from a few sources. Either the secondary limit (TCO2) is energizing it; in which case the switch is either overheated or stuck; or the economiser is calling for fan for some reason, or the fan delay relay is stuck or incorrectly energized. I would bypass the economizer to rule it out and then see where your IDF contactor is getting energized from by checking for voltage through your TCO2 and FDR from terminals 1 and 2.
01-25-2013, 04:13 PM #7
01-25-2013, 04:37 PM #8
- Aug 2012
- Los Angeles
- 18
Will try that and get back to you guys
01-25-2013, 04:41 PM #9
IDF is indoor fan or induced draft fan???
WWFD
01-25-2013, 04:52 PM #10
- Aug 2012
- Los Angeles
- 18
Idfm, indoor fan motor
01-25-2013, 05:23 PM #11
Well my bad then. I thought that stood for induced draft fan motor in your post.
01-25-2013, 05:52 PM #12
Mine too.
WWFD
01-25-2013, 08:01 PM #13
is it on EMS?