    carrier clo

    I have a carrier split model 38QRR048-501 that takes care of a server room. Problem is if the building looses power and stitch's to generator in 7 sec, i lock out on the clo. I need to put a time delay on break, but would like to hear any ideas. Thanks in advance

  2. #2
    Join Date
    Mar 2007
    Location
    South Texas
    Posts
    239
    Post Likes
    install a icm voltage monitor and set it up for auto rest