Freezestat Questions Pro/Cons
Dear Sir,
Commercial Manual Reset Freezstat application, unit shuts down and preheat valve full open. But some say chill water valve shall open too? Skeptical.
Please help feedback appreciated. Pro/Con's for the units mentioned, they have preheat coil (some steam, some hw coils) and CC in main unit, no reheat at unit:
1) Rooftop AHU's that have SF and RF that serve VAV's.
2) AHU's that have SF and RF that serve VAV's in mers.
3) 100% OA Units. Supply Fan no return. Just exhaust in space to supplement for not having return.
Respectfully need your expertise and experience,
Bob C
-
01-24-2013, 06:33 PM #2
Professional Member
- Join Date
- Feb 2008
- Location
- Jerzee
- Posts
- 32
Chilled water valve should open also. Be sure both hot water and chilled water pumps are running.
-
01-24-2013, 07:11 PM #3
In freeze condition you should be circulating your chilled water or coil is drained completely. Ideally adding a freeze pump to circulate the water in your chilled water coil.
-
01-25-2013, 06:57 AM #4
Regular Guest
- Join Date
- Jul 2011
- Location
- NEW YORK
- Posts
- 51
If you have a chw pump that is running all year long. Do you still reccommend a freeze pump? Maybe on 100% OA units that have Preheat Coil, Hum Coil and Chill Water Coil. No reheats only in space.
Any Negs about opening the CHW Valve too? At all that you can think of?
-
01-25-2013, 07:59 AM #5
The only con I can think of is cost. There should not be much need for CW freeze pump if you have a properly installed fstat and glycol in the system already. If the existing CW valves are spring return currently, I would spring them open. Otherwise I would leave them as is and worry more about the HW valve, coil pumps, fans, and dampers.
Propagating the formula. http://www.noagendashow.com/
-
01-25-2013, 08:05 AM #6
Regular Guest
- Join Date
- Jul 2011
- Location
- NEW YORK
- Posts
- 51
Have some steam preheat coils too.
-
01-25-2013, 12:15 PM #7
Professional Member
- Join Date
- Oct 2005
- Posts
- 309
-
01-25-2013, 12:17 PM #8
Professional Member
- Join Date
- Oct 2005
- Posts
- 309
-
01-24-2013, 08:14 PM #9
Professional Member
- Join Date
- Mar 2008
- Location
- Kitchener, Ontario
- Posts
- 491
I would typically open both valves to verify water is circulating, Hopefully do to the risk of freezing the system that they have added glycol, some don't prefer to add due to the loss of heat transfer.
-
01-24-2013, 08:21 PM #10
Professional Member
- Join Date
- Oct 2005
- Posts
- 309
Like they said, opening the cooling valve is good but doesn't help without a freeze pump or unless the main pump runs in the winter. You could also command the main pump on when there is a freezestat alarm if there is a BMS and not just local controls.
For what it's worth, Honeywell lawyers (and there were lots of them!) always insisted the device be called a "safety low limit". "Freezestat" could imply it can prevent freezing, which it can't.
-
01-25-2013, 12:16 AM #11
Ditto. It’s rare to see coil pumps on CW coils and even less likely to see the CW pumps running in the winter. Sure you could kick everything on during a trip, ASSUMING your actually monitoring the fstat verses just hardwiring them.
If the HW system has hot water flow and the HW valve fails open, fans off, econ closed….it should make little difference if the CW valve also opens. With no HW flow, the CW coil is likely to freeze regardless here.
Compared to the energy costs of running the CW pumping system all winter, I would think glycol would be a more cost effective solution. Isolating and draining the CW coils is also not an uncommon solution.
At a minimum, we use fail safe actuators on all HW coils with possible exposure to OA and economizers. Hardwire the fstat to the actuators and fans. If monitoring of the fstat is required, it’s a DPDT fstat or a relay on the main shutdown circuit fed back into the BMS. Through software, we open the CW valve if equipped. IMHO this will cover all but the most extreme failures and prevent the coils from freezing.
If they want more protection, we certainly provide it.Propagating the formula. http://www.noagendashow.com/
-
01-29-2013, 09:00 AM #12
Regular Guest
- Join Date
- Jul 2011
- Location
- NEW YORK
- Posts
- 51
What about 100% OA Units? With Steam preheat no reheat. Still recommend just preheat valve to open?
-
01-29-2013, 09:01 AM #13
Regular Guest
- Join Date
- Jul 2011
- Location
- NEW YORK
- Posts
- 51
What about a) Roof Top Units and b) 100% OA Roof Top Units? With Steam preheat no reheat. Still recommend just preheat valve to open?